Can I run Romex through conduit?
Old 03-05-14, 09:14 PM
N
Received 1 Upvote on 1 Post
I have some wiring running to a switch and lights that supposed to be run through conduit but currently has Romex running to it. My question is can I just pull that existing Romex through the conduit when I put the conduit in place (assuming I disconnect the Romex on one end and pull it through), or do I need to replace the Romex with two or three wire wiring?
Old 03-05-14, 09:17 PM
Nashkat1's Avatar
Received 5 Upvotes on 4 Posts
Will the conduit be closed (run from one box to another) or will it be a sleeve (open on one end)?
Old 03-05-14, 09:22 PM
N
It would be closed, one box to another, e.g., from a porcelain light circuit box to a switch box. What's the difference between that versus being open on one end? Thanks.
Old 03-05-14, 09:34 PM
ray2047's Avatar
Best practice is to use individual conductors (THHN/THWN)in a closed system. Are you in Chicago? If so the inspector may not want to see cable.
Old 03-06-14, 06:01 PM
CasualJoe's Avatar
Received 178 Upvotes on 161 Posts
The NEC does not prohibit running NM cable (aka romex) in conduit, but like Ray said, best practice is to use individual conductors. Some AHJs, however, will not allow a cable assembly to be installed in conduit except for a short sleeve to protect the cable from damage.
Old 03-06-14, 07:06 PM
pcboss's Avatar
Received 177 Upvotes on 155 Posts
The conduit would need to be larger for the cable than for individual conductors.
Old 03-06-14, 07:27 PM
Nashkat1's Avatar
Heat. Type NM is designed to be installed in an environment where the heat can get away from it.