I am installing three wall sconces and was wondering if I could bring power to the switch, then go up to a junction box, that has one 12/2 going to each fixture, rather than having two go to each one? If so, I assuming I join all the blacks together and all the whites in the junction box?

Thanks
 
Sponsored Links
  #2  
Old 03-08-14, 06:39 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,991
Welcome to the forums!

What you describe would work, however the junction box would be required to be permanently accessible. You could just run a switch leg from the switch box, to each light fixture box, if the switch box is big enough (cubic inches), or just daisy chain the fixture boxes like this:

Switch box------> light--------> light--------> light
 
  #3  
Old 03-08-14, 07:55 AM
Member
Thread Starter
Join Date: Mar 2014
Posts: 3
I wanted to wire it whatever way would prevent me from running two romex cables to the first two lights, however I will if I have to
 
  #4  
Old 03-08-14, 08:28 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,512
You can use a single cable from a junction box to each scone but like Tolyn mentioned.... the junction box would need to be installed where it was always accessible.
 

Last edited by ray2047; 03-08-14 at 09:00 AM. Reason: wire>cable
  #5  
Old 03-08-14, 11:53 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,991
Is there a reason you do not want multiple cables in the light boxes? Most cases it is easier to daisy chain lights.
 
  #6  
Old 03-08-14, 12:03 PM
Member
Thread Starter
Join Date: Mar 2014
Posts: 3
I thought it would be harder to daisy chain it, rather than just run one romex up to a central point, then add the power from the switch. All you guys think the daisy chain is easier?
 
  #7  
Old 03-08-14, 12:34 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,991
As long as the fixture boxes have enough cubic inch capacity (at least 14 CI), yes. Having a junction box is more work than it is worth.
 