sub panel feed question


  #1  
Old 03-10-14, 04:12 PM
R
Member
Thread Starter
Join Date: Nov 2004
Location: xxx
Posts: 308
Upvotes: 0
Received 0 Upvotes on 0 Posts
sub panel feed question

We have a 200amp main entry panel, outside and downstairs. It also feeds a few yard circuits, and a 100 amp sub panel.

Is the sub panel fed by a four wire setup? Neutral, ground, and two hots for 120v/240v service? If this is correct, then I assume the hots are 2 gauge wires.
 
  #2  
Old 03-10-14, 04:32 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
Is the sub panel fed by a four wire setup?
It should be.

Neutral, ground, and two hots for 120v/240v service?
That would be correct.

If this is correct, then I assume the hots are 2 gauge wires.
They might be. The size of the wires would be dependent on the size of the breaker feeding them, whether they are copper or aluminum and the overall length of the feeder.
 
 