EMT Conduit Question

I recently installed a new circuit in my garage. I ran EMT 1/2 inch conduit from the garage wall, where the wiring enters the garage, to the outlets it powers. I did NOT strip the outer sheathing away from my 12-2 NM wiring before running it through the conduit. Now that it's installed and working, I've read a few places that you're supposed to strip away that outer sheating. The reason being given is that the 12-2 NM wiring may overheat due to being sealed inside the metal conduit.

My question is, do I need to re-visit my project and remove the outer sheathing? Or should I be okay as is?

Other info: The circuit is dedicated to the garage, 20 amp breaker, and is only feeding GFCI outlets. Everything is indoors, no dampness in my garage. I've grounded the outlet boxes to the wiring and used a tester to ensure the GFCIs are wired properly and open as expected. However, I'm pretty new to this DIY work, so let me know if something sounds off.

Thanks!
 
  #2  
Old 03-10-14, 12:39 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
Conduit with cable installed inside it is typically done for physical protection against damage as a sleeve. You could have used individual conductors in a complete conduit system.

Stripping the sheath off removes the listing of NM cable and means it no longer meets the code requirements.
 
  #3  
Old 03-10-14, 04:00 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
Although the NEC doesn't prohibit running NM cable in conduit, it's not a normal practice and some jurisdictions will not allow it because it's a cable assembly. It's also the mark of an inexperienced DIYer and not a professional.
 
  #4  
Old 03-10-14, 05:16 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Is this an attached or detached garage?
 
  #5  
Old 03-10-14, 07:31 PM
S
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Attached garage.

CasualJoe - What type of wire should I have used in the conduit? And yes, I'm an inexperienced DIYer. Thanks!
 
  #6  
Old 03-10-14, 07:40 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
THHN wire would be fine in a complete conduit system.
 
  #7  
Old 03-10-14, 07:56 PM
R
Member
Join Date: Dec 2005
Location: USA
Posts: 644
Upvotes: 0
Received 65 Upvotes on 50 Posts
OK I have to ask, what is the difference between if the sheath is removed from NM cable and THHN?
 
  #8  
Old 03-10-14, 07:59 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
THHN is labeled. The conductors inside NM are not.
 
  #9  
Old 03-11-14, 08:02 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
THHN wire would be fine in a complete conduit system.
There are other types of wire also acceptable, but THHN is the most widely accepted and available wire to use.
 
  #10  
Old 03-12-14, 08:03 AM
S
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Okay, easy enough. Thanks for the advice everyone!
 
 