Hi everyone. I have a range with a fairly standard cord and male plug - like this one Shop Utilitech 50-Amp 125/250-Volt Black 3-Wire Plug at Lowes.com
However, in the kitchen my house has a different receptacle, like this one - Shop Utilitech 50-Amp Surface-Mount Appliance Electrical Outlet at Lowes.com which I have never seen in a kitchen before.
The big box home improvement stores don't seem to have a ready-made solution, and it's looking like I may end up doing some wiring. I'd rather change the plug on the range if possible. What is the easiest way to go about this? Thanks everyone!
Old 03-12-14, 07:15 AM
P
Received 2,112 Upvotes on 1,891 Posts
The cord on the stove can be pretty easily replaced. Generally there is a separate, removable cover so you don't have to remove the entire back to get at the connections.
Many appliances are not sold with a cord and the correct one must be purchased and installed to match the house. It's also a common problem with dryers as older houses have a 3 hole receptacle and newer have 4.
Old 03-12-14, 08:07 AM
ray2047's Avatar
Is this the receptacle you have:
If so it is a 240 volt grounded receptacle. You need a 120/240 3 wire receptacle. You need to open the receptacle and see if you have white, black, red. If you do have a NEMA 6-50R and the wires are correct replace with the correct receptacle, NEMA 10-50R. If you have white black bare the wiring is not code compliant.
Assumes you don't have metal conduit.
Old 03-12-14, 08:11 AM
A
Received 92 Upvotes on 84 Posts
That wall receptacle looks like a 240 only that is not meant for a range. Should be replaced with standard 10-50R. Take cover off and verify that there are only 3 wires. If 4 then should use 14-50R
Old 03-13-14, 09:21 AM
T
I cut the power and took a look this morning. I have what looked to be red and black (although the insulation was dirty so I am probably mistaken) and a bare wire. The house is from 1960, though the receptacle was clearly installed recently. Incidentally, my oven is from 1960 as well.
Old 03-13-14, 11:21 AM
ray2047's Avatar
Sounds like 2-conductor SE. That was probably never code compliant. You need to run a new 6-3 NM-b cable (white, black, red, bare), install a NEMA 14-50 receptacle, and change the cord on the stove to a 14-50 four prong plug. Follow the manufactures instructions for converting the stove to four wire.
Old 03-13-14, 12:14 PM
T
Just realized there was some ambiguity in my previous post when describing the wires. There are two insulated wires and a third, un-insulated wire that I take to be the ground.
Old 03-13-14, 12:24 PM
ray2047's Avatar
Yes, I understood your post.
Old 03-13-14, 12:44 PM
A
SE was allowed as long as going back to main panel.
Just change outlet to this and be done with it. Shop Cooper Wiring Devices 50-Amp Surface-Mount Appliance Electrical Outlet at Lowes.com
Old 03-13-14, 01:03 PM
ray2047's Avatar
Please cite code that allows bare neutral in this situation.
Old 03-13-14, 08:14 PM
A
2011 NEC 250.140
Exception: For existing branch-circuit installations only where an equipment grounding conductor is not present in the outlet or junction box, the frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be permitted to be connected to the grounded circuit conductor if all of the following conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.
(2) The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.
(4) Grounding contacts of receptacle furnished as part of the equipment are bonded to the equipment.
Old 03-13-14, 08:29 PM
pcboss's Avatar
Received 194 Upvotes on 170 Posts
SE cable could be used for a range. Two wire +ground NM was not legal for a stove.
Old 03-13-14, 08:56 PM
ray2047's Avatar
Thank you for the clarification.
Old 03-14-14, 10:56 AM
CasualJoe's Avatar
Received 185 Upvotes on 166 Posts
Nor was it ever legal for a dryer, but I sure used to see it a lot 30 years ago and occasionally still see an older installation with it.
Old 03-14-14, 11:14 AM
ray2047's Avatar
I know now I was wrong to question the SE but NM not being compliant and SE being compliant seems such a contradiction... and again the NEC authors manage to puzzle us.