Electrical radiant heat in the ceiling

I took down a wall between two small bedrooms to create one large bedroom. Both bedrooms have electric radiant heat in the ceiling thus I had 2 thermostats 1 controlling each side. Does anyone know if I can change out the old ones with a new one that would control both sections of the ceiling?
 
  #2  
Old 03-13-14, 04:01 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Are the thermostats line voltage? If so how many amps/watts on each thermostat?
 
  #3  
Old 03-13-14, 04:23 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,245
Received 110 Votes on 96 Posts
I would doubt that you could combine the two systems easily. Do you have access above the ceiling?
 
  #4  
Old 03-15-14, 09:51 AM
7
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
I do have access above the ceiling into the attic.
 
  #5  
Old 03-15-14, 10:01 AM
7
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Both thermostats are fed from a single piece of Romax (one pigtailed to the other) from the panel and attached to two pinned 20 amp breakers. Each thermostat is rated at 22 amps.
 
  #6  
Old 03-15-14, 10:19 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,436
Received 1,408 Votes on 1,303 Posts
Good detective work

Since both heat panels are currently running on a single two pole 20A breaker then you can use one thermostat to control both. Using one of those 22A thermostats would be fine.
 
 