Moving a 240v outlet

At a relative's home we added a 200A sub-panel to a centrally-located laundry room. One of the new circuits we installed is a 240v dryer outlet that has about 15ft of 10/3 NM-B wire running to it. Since they have a gas dryer the outlet has never been used.

Now (3 years later) they buy a 240v welder that needs it's own circuit. I want to move the outlet from the laundry room to a shed. The length of wire needed should be approx 80ft. My questions/concerns are:

1. Can I splice onto the end of the 15ft existing wire (after removing the outlet) or should I start with new wire at the panel? The splice would be for convenience, as it is already headed in the right direction.

2. Is 80' of 10/3 good enough to run a welder (sorry, no specs) or should 8/3 used instead?

3. Would adding a dedicated ground near the new outlet be a good idea?

Thanks in advance for your time and input.
 
Sponsored Links
  #2  
Old 03-14-14, 02:45 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,948
Received 32 Votes on 27 Posts
The receptacle for the welder will already be grounded. You do not need a second ground.

Type NM cable cannot be used outdoors.

Many welders are 240 volt only and use xx-2 cable, not xx-3 like you have.
 
  #3  
Old 03-14-14, 02:57 AM
Member
Thread Starter
Join Date: Mar 2014
Posts: 2
Received 0 Votes on 0 Posts
Crap, I should've known that! Thanks for the quick reply.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: