Neutral in not grounded for all four outlets in the same breaker
Four outlets in the same breaker stopped working. I used multimeter to check AC voltages for those outlets. Ground to Neutral reads 19V and Ground to Hot reads 120V. Neutral to Hot reads about 100V. The readings are same for those non-working outlets. Working outlets read 0V from ground to neutrals. It seems non-working outlets has non-grounded neutral plugs. How do I fix this?
#2
It seems non-working outlets has non-grounded neutral plugs
Neutral to Hot reads about 100V.
#3
Member
Thread Starter
Join Date: Mar 2014
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Called electrician. There was an another outlet that belongs to the same breaker. That outlet has been always working and it was not nearby those non-working outlets, so I never checked that outlet before. We found the neural wire was loose on that receptacle and hot wire also showed some burnt spot. Replaced that receptacle and problem solved..