GFCI needed


  #1  
Old 03-17-14, 04:17 PM
G
Member
Thread Starter
Join Date: Jun 2012
Posts: 73
Upvotes: 0
Received 0 Upvotes on 0 Posts
GFCI needed

Can anyone tell me if a GFCI is needed in this pict
[ATTACH=CONFIG]28480[/ATTACH]
 
Attached Images  
  #2  
Old 03-17-14, 04:36 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
GFI protection is only required within 6' of a laundry tub. You do not need it unless there is also a tub in the room outside of your picture.
 
  #3  
Old 03-17-14, 04:39 PM
G
Member
Thread Starter
Join Date: Jun 2012
Posts: 73
Upvotes: 0
Received 0 Upvotes on 0 Posts
There is not a tub was just curious about the hookups to the washer so close to it. I do appreciate our help
 
  #4  
Old 03-17-14, 07:04 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
Can anyone tell me if a GFCI is needed in this pict
If the laundry unit is in an unfinished basement it would need to be a GFCI receptacle. Is the picture in an unfinished basement?
 
  #5  
Old 03-17-14, 07:17 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
Good point Joe. I saw the drywall and didn't think about the rest of the basement.
 
  #6  
Old 03-17-14, 08:16 PM
G
Member
Thread Starter
Join Date: Jun 2012
Posts: 73
Upvotes: 0
Received 0 Upvotes on 0 Posts
Its not in an unfinished basement its a very small finished laundry room
 
  #7  
Old 03-18-14, 05:07 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
I believe I read somewhere that the 2014 NEC is going to require GFCI protection on all washer receptacles, but I have no reference for that. For most of us, what we now have would be grandfathered except some local jurisdictions may require it right away.
 
  #8  
Old 03-18-14, 10:55 AM
M
Member
Join Date: Jul 2007
Location: USA
Posts: 436
Received 1 Upvote on 1 Post
Sorry for the partial hijack, but why would "finished vs. unfinished" basement make a difference in whether or not a GFCI is required?
(I'm not challenging the idea, just looking for the reasoning in the code, so I can learn!!)
 
  #9  
Old 03-18-14, 11:06 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
GFI protection is required by the electrical code for unfinished basements. If the basement is finished it is not required.
 
  #10  
Old 03-18-14, 02:42 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
As a clarification, a "finished" basement has some kind of floor covering over the concrete, an "unfinished" basement has just the concrete (or dirt) floor.
 
  #11  
Old 03-19-14, 06:04 AM
K
Member
Join Date: Aug 2013
Posts: 258
Received 1 Upvote on 1 Post
Furd
As a clarification, a "finished" basement has some kind of floor covering over the concrete, an "unfinished" basement has just the concrete (or dirt) floor.
So an insulated basement with Gyprock walls tops to bottom, but a painted concrete floor is considered unfinished for NEC wiring purposes?
 
  #12  
Old 03-19-14, 07:47 AM
M
Join Date: Dec 2012
Posts: 397
Upvotes: 0
Received 0 Upvotes on 0 Posts
So an insulated basement with Gyprock walls tops to bottom, but a painted concrete floor is considered unfinished for NEC wiring purposes?
That does make a little more sense, since being on concrete is more likely to hurt you than being on carpet in case of a horrible shock, whereas having drywall up never struck me as a reason to have GFCI. I'd never even considered it that way until you asked the questions, Kiton.

Doesn't meet the common popular understanding of "finished", though.
 
 