Is this panel dangerous? Do I need to replace?
#1
Member
Thread Starter
Join Date: Mar 2014
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Is this panel dangerous? Do I need to replace?
I am thinking that I might need to replace this panel. House lights dim a bit when washer or dryer go on. I showed these pics to someone with some knowledge and he indicated the blue and red switches are dangerous. He said the connectors were like splitters and I am drawing more power than the panel can supply and those can actual start to melt. Dimming light might be a sign of melting starting. Now he has only seen the pictures too, but I was wondering if anyone had experience with these switches or might be able to confirm what I was told. Any ideas are appreciated.

#2
Welcome to the forums.
Red and blue breakers aren't dangerous as such. I only remember Bryant using those colored breakers and those aren't Bryant. There should be a brand name on or inside the cover.
Breakers don't necessarily cause lights to dim. That could be caused by many things including your main service and how it's set up.
Red and blue breakers aren't dangerous as such. I only remember Bryant using those colored breakers and those aren't Bryant. There should be a brand name on or inside the cover.
Breakers don't necessarily cause lights to dim. That could be caused by many things including your main service and how it's set up.
#3
Red and blue breakers aren't dangerous as such. I only remember Bryant using those colored breakers and those aren't Bryant. There should be a brand name on or inside the cover.
#8
That's a Crouse-Hinds/Murray division panel. It's an older panel but I'm not aware of any inherent problems with them. It's only a 12 circuit panel with lots of tandem breakers.
The top four breaker spaces are rated for full size breakers and the bottom eight spaces are rated for tandems so the panel has been breakered properly.
I don't know the bus material.
The top four breaker spaces are rated for full size breakers and the bottom eight spaces are rated for tandems so the panel has been breakered properly.
I don't know the bus material.
#9
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Considering its age and being an aluminum buss panel, I'd recommend changing it.
Now, IF this panel and circuit breakers is one of those with a known history of failure, like the Zinsco, I would have a different opinion, but this is a Murray panel and while the Murray was a less-expensive panel in its day it was still completely functional and had no more failures (that i am aware of) than the copper-bus panels.
#13
Member
Thread Starter
Join Date: Mar 2014
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
here is a label on the red/blue breakers
This is the label on the breakers. Reads Murray 2 pole unit, Issue KR-840, CTL-Style MM, CU/AL.

Last edited by PJmax; 03-19-14 at 05:52 PM. Reason: Fixed picture
#14
Member
Thread Starter
Join Date: Mar 2014
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
opinion
So again, the guy I was talking to, who only saw pictures of the red and blue breakers, said that the breakers are pretty dangerous and are against code here. He said that the connectors are basically like splitters and I am drawing more power than the panel can give and the panel will try to supply that demand and can actually melt. He was very concerned and said I should have someone take a look at it.
Not holding anyone to anything, but from the pics I have attached, can anyone comment or agree on what was suggested to me?
Not holding anyone to anything, but from the pics I have attached, can anyone comment or agree on what was suggested to me?
#15
Color of breakers don't matter.
No clue what connectors he means are splitters or what he means by that. If he means some breakers have two wires and are not rated for two wires that is a problem that needs to be corrected but it is easy to correct. Note:It is not uncommon for the total of the individual breakers to add up to 150%-200% of the panel rating and that is okay because breakers are not normally run at full load or even half load.
He said that the connectors are basically like splitters and I am drawing more power than the panel can give and the panel will try to supply that demand and can actually melt.
#16
The guy you are talking to is on crack. 
Really, from what I see you just have a perfectly fine older Murry panel. Although some of the breakers look like General Switch and maybe one ITE. Your dimming lights could be nothing other then the quick jump in load when you start a motor. Motors can draw up to 300% of full load current.
A branch circuit can not draw more amps than the breaker protecting it is rated for. The entire panel will not provide more amps than the main breaker is rated for. So if you had a load of 10 amps on each branch circuit in the panel, the branch circuit breakers would not trip, but the main would.
Aluminum bus panels are still installed today and are just fins and safe. If your concerned that the panel is showing problems, turn off the main breaker, remove each branch circuit breaker and inspect the bus and see if you see signs of pitting/melting. While your there, make sure all the connections in the panel are tight, EXCEPT the ones to the main breaker. Those connections are always hot!! If your are not comfortable with any of the above, please call an electrician. We want you to keep coming back.

Really, from what I see you just have a perfectly fine older Murry panel. Although some of the breakers look like General Switch and maybe one ITE. Your dimming lights could be nothing other then the quick jump in load when you start a motor. Motors can draw up to 300% of full load current.
A branch circuit can not draw more amps than the breaker protecting it is rated for. The entire panel will not provide more amps than the main breaker is rated for. So if you had a load of 10 amps on each branch circuit in the panel, the branch circuit breakers would not trip, but the main would.
Aluminum bus panels are still installed today and are just fins and safe. If your concerned that the panel is showing problems, turn off the main breaker, remove each branch circuit breaker and inspect the bus and see if you see signs of pitting/melting. While your there, make sure all the connections in the panel are tight, EXCEPT the ones to the main breaker. Those connections are always hot!! If your are not comfortable with any of the above, please call an electrician. We want you to keep coming back.

#17
I fixed your pics so that were easier to see. I took your inside panel one and enlarged it. I only see one issue and that's a single wire all the way at the top in a two pole breaker. Certainly no fire issue.
I don't see any wires doubled up on a breaker. I see spare breakers. I see a two pole 100A breaker which must mean you have a sub panel somewhere.
I circled the two connections at the top of the panel in red. Those two connections on the main breaker are always live even when main breaker is off. I don't see anything that would raise a red flag here.
I don't see any wires doubled up on a breaker. I see spare breakers. I see a two pole 100A breaker which must mean you have a sub panel somewhere.
I circled the two connections at the top of the panel in red. Those two connections on the main breaker are always live even when main breaker is off. I don't see anything that would raise a red flag here.

#18
the guy I was talking to, who only saw pictures of the red and blue breakers, said that the breakers are pretty dangerous and are against code here. He said that the connectors are basically like splitters and I am drawing more power than the panel can give and the panel will try to supply that demand and can actually melt.
The only thing I see that seems a bit odd is in the picture in your post #4. The main breaker is "ON" when down and "OFF" when up. I don't believe I have ever seen a main breaker like that.
#20
The only thing I see that seems a bit odd is in the picture in your post #4. The main breaker is "ON" when down and "OFF" when up. I don't believe I have ever seen a main breaker like that.
#21
Banned. Rule And/Or Policy Violation
Join Date: Jan 2010
Location: KS
Posts: 1,655
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So again, the guy I was talking to, who only saw pictures of the red and blue breakers, said that the breakers are pretty dangerous and are against code here. He said that the connectors are basically like splitters and I am drawing more power than the panel can give and the panel will try to supply that demand and can actually melt. He was very concerned and said I should have someone take a look at it.
Not holding anyone to anything, but from the pics I have attached, can anyone comment or agree on what was suggested to me?
Not holding anyone to anything, but from the pics I have attached, can anyone comment or agree on what was suggested to me?
#22
Banned. Rule And/Or Policy Violation
Join Date: Jan 2010
Location: KS
Posts: 1,655
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It just hit me what he must have meant. You have some tandem breakers in the panel. A tandem breaker is actually two single pole breakers within one molded case and both circuits draw power from the same bus stab. I believe he is thinking of the tandem breaker like it is splitting the power from the one bus stab, which it basically is, but that's pretty typical. Tandem breakers are still widely used today with few problems.
#23
It may have been designed as a bottom fed panel.
Every 100A Murray panel I've ever seen in person had the main breaker upside-down. It is essentially a back-fed main and even has a retaining piece.
#24
But as PJ already mentioned, that panel is designed to take tandems in the bottom 8 slots.. It's not like someone installed a bunch of non-CTL replacement tandems in a panel not designed for it. The guy's just a dope.
#25
I seem to remember an HI from Illinois saying that tandems are not accepted in their area even though the panel is listed for them. I am getting that vibe from this thread. Just another quirk.
#26
Member
Thread Starter
Join Date: Mar 2014
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
That sounds like what might be going on, since I know he talked about code and he apparently knows the rules books pretty clearly. I might have this guy over to get the words straight from him regarding what he thinks he is seeing and then post back here. Everyone has been pretty clear on what they see, even if just from pictures. I WILL NOT be sold anything at this time. Any ideas on what to do with the lights that briefly dim when a/c, dryer, washer first start? Do I really need to care about this?
#27
Do I really need to care about this?
About the use of tandem breakers, that should be investigated. Based on the age of your panel, even if tandem breakers are not allowed now, your panel may be grandfathered in.