Wiring from Main House to Garage Sub-Panel

The Current Situation:
I have a 30 amp breaker in the main panel in the house. This is currently feeding 110 to a sub-panel in the garage. The garage sub-panel currently houses 3 single-pole breakers (1 15-amp and 2 20amp)

The Future Situation:
I want to upgrade the breaker in the main panel to a 60-amp breaker to feed the sub-panel in the garage. I also want to run new wire to carry 220 to the sub-panel in the garage. I want to install a 30-amp dual-pole breaker in the garage sub-panel to bring power to a cadet heater and an outlet.

The distance of wire I'm going to need between the house and the garage panels is going to be 70'. What gauge of wire will I need to span this distance?
 
Attached Images   
Sponsored Links
  #2  
Old 03-21-14, 09:39 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,539
Received 408 Votes on 384 Posts
If we assume that the garage is attached to the house.......

With the addition of a two pole 60A breaker you'll need to run 6-3 w/gr NM or MC type cable between the main panel and the sub panel.
 
  #3  
Old 03-21-14, 09:44 AM
Member
Thread Starter
Join Date: May 2013
Location: USA
Posts: 25
Received 0 Votes on 0 Posts
The garage is not attached to the house. However, part of the run is under the house in a crawlspace and the remainder of the run is through schedule 40 conduit, so the wire is never in an exterior condition.

I assumed that there is a voltage drop over that large of a distance which would require an increase in wire gauge.
 
  #4  
Old 03-21-14, 12:41 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Conduit outside is considered a wet location no matter how well sealed so just run THWN all the way in conduit. Running cable in conduit is no necessary except for example for short sleeves to protect it where it enters and leaves the ground. One hundred feet or less no need to worry about voltage drop.
 
  #5  
Old 03-21-14, 12:45 PM
Member
Thread Starter
Join Date: May 2013
Location: USA
Posts: 25
Received 0 Votes on 0 Posts
So is PJ's suggestion of 6ga wire going to be sufficient?
 
  #6  
Old 03-21-14, 06:55 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,092
Received 29 Votes on 23 Posts
So is PJ's suggestion of 6ga wire going to be sufficient?
Yes, but not NM or MC cable. If you use cable it must be UF cable, but I'd do like Ray suggested and run THWN conductors in conduit all the way. You'll need 3 - #6s and 1 - #10 ground. You'll need to add an auxilliary ground bar in the subpanel and install one or two ground rods at least 6 feet apart and connect them to the ground bar with #6 copper, bare or insulated. I prefer bare. The neutral bar should not be bonded to the box and only neutral wires terminate on the neutral bar. The ground wires will terminate on the ground bar.
 
  #7  
Old 03-21-14, 07:32 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,955
Received 33 Votes on 28 Posts
Depending on the size of the conduit you may not be able to upgrade the feeder.

Also that is a split bus panel the bottom section is limited to most likely 60 amps.
 
  #8  
Old 03-22-14, 02:47 PM
Member
Thread Starter
Join Date: May 2013
Location: USA
Posts: 25
Received 0 Votes on 0 Posts
So, in this application is it necessary to run 4 individual wires or am I able to use a cable such as this:

#6-3 THHN-PVC Tray Cable with Ground
 
  #9  
Old 03-22-14, 03:33 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
That is a special purpose cable. You would use UF-b. Best practice is not to run UF-b in conduit except for short sections to protect it such as when it enters and leaves the ground.
 
  #10  
Old 03-22-14, 07:47 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,092
Received 29 Votes on 23 Posts
So, in this application is it necessary to run 4 individual wires or am I able to use a cable such as this:

#6-3 THHN-PVC Tray Cable with Ground
That tray cable is also approved for direct burial. When tray cable is the cheapest option, there is usually a catch.
 
  #11  
Old 03-22-14, 09:38 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
When tray cable is the cheapest option, there is usually a catch.
Looked like 3-phase without a neutral and since #6 can't be remarked that could be the catch.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: