electrical landscape question

Its spring afterall!

Got a new service. Electricians drove a ground rod outside. They went just a little lower than grade. I am afraid when I lay new mulch it will cover the acorn clamp and some of the wire. If I lay topsoil, it will also cover the connection.


Is that ok? What can I do in this case?
And how does the bare copper not deteriorate so close, or in contact, with the ground?
 
Sponsored Links
  #2  
Old 03-21-14, 02:41 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,144
Received 83 Votes on 71 Posts
The connections need to be flush or below grade. As long as they are listed for direct burial you should have no issues.
 
  #3  
Old 03-21-14, 03:15 PM
M
Member
Thread Starter
Join Date: Nov 2013
Posts: 365
Received 0 Votes on 0 Posts
I can bury the bare stranded #8 wire?
 
  #4  
Old 03-21-14, 03:39 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,598
Received 200 Votes on 178 Posts
Yes.
----------------------------
 
  #5  
Old 03-21-14, 04:31 PM
M
Member
Thread Starter
Join Date: Nov 2013
Posts: 365
Received 0 Votes on 0 Posts
I also noticed where they made the connection, with the screw compression, the stranded wire kind of flattened out, the strands aren't tightly twisted under that acorn clamp... does that sound like an issue?

As far as burying it, I will do so, I trust you guys but that seems weird that its allowed to deteriorate in the ground like that....
 
  #6  
Old 03-21-14, 06:21 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,144
Received 83 Votes on 71 Posts
It is not going to deteriorate.
 
  #7  
Old 03-21-14, 06:28 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,638
Received 83 Votes on 73 Posts
I can bury the bare stranded #8 wire?
#8 to the ground rod? ....................
 
  #8  
Old 03-21-14, 06:34 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,144
Received 83 Votes on 71 Posts
That sounds too small, although it is never required to be larger than #6.
 
  #9  
Old 03-22-14, 12:27 PM
Z
Member
Join Date: Oct 2013
Posts: 592
Received 0 Votes on 0 Posts
I just ran a GEC for a garage subpanel. Using 'Table 250.66' said I can use #8 ... what am I missing?


Good luck with the landscaping mummy.

PC BOSS That sounds too small, although it is never required to be larger than #6.
 
  #10  
Old 03-22-14, 12:37 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,598
Received 200 Votes on 178 Posts
what am I missing
Your missing 250.64(B) Securing and protection from physical damage. "Grounding electrode conductors smaller than #6 AWG shall be in RMC, IMC, PVC, EMT, or cable armor"

#6 you can just run along the building surface as long as it is free from physical damage.
 
  #11  
Old 03-22-14, 12:48 PM
Z
Member
Join Date: Oct 2013
Posts: 592
Received 0 Votes on 0 Posts
No, I wasn't missing that. I ran it in pvc. The original poster didn't say it was ran in conduit or not but I would assume if an electrician did it, then the #8 is also in conduit.

I think the OP was concerned about the exposed portion at the rod/acorn clamp. Which now that I think of it in regards to my similar setup, its a valid concern about covering up the smaller wire with dirt.
 
  #12  
Old 03-22-14, 06:27 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,638
Received 83 Votes on 73 Posts
The original poster didn't say it was ran in conduit or not but I would assume if an electrician did it, then the #8 is also in conduit.
Contractors are in business to make money. Considering the labor to install the conduit, a smart contractor would run #6 without the conduit and everyone wins.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: