How bad is this?




New 200 amp main lug panel in a church hall remodel. 200 amp service. 200 amp disconnect outside feeding 3 wire 4/0 Al to a 200 amp panel which feeds everything. Kitchen has two double ovens, one freestanding stove/oven and one stovetop plus two microwaves. Electric hot water and two 4ton-ish air conditioners.

Im pretty sure those lugs are going to burn off the first Sunday the kitchen gets used, but I what do I know.
 
Sponsored Links
  #2  
Old 03-24-14, 05:42 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,590
The issue is that we no longer know the ampacity of the conductors. They may now be too small for the expected load.
 
  #3  
Old 03-24-14, 05:47 PM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 118
Almost forgot the commercial dish washer.
 
  #4  
Old 03-24-14, 05:51 PM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 118
What is 4/0 AL rated at with 13-15 strands trimmed off in order to fit in 2/0 lugs?
 
  #5  
Old 03-24-14, 05:59 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,590
The is no way to know the remaining ampacity. It needs to be fixed.
 
  #6  
Old 03-24-14, 07:32 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,284
I find it odd that a 200 amp panel would not have lugs big enough for 4/0 wire. Especially a newer one like the Square D Homeline you have. Most panels rated for 200 amps will have lugs rated for 250 MCM or larger as a 200 amp residential service will require 4/0 aluminum. Are you sure that panel is rated for 200 amps?
 
  #7  
Old 03-24-14, 07:38 PM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 118
Im not sure what the rating is. I think it was converted from a main breaker panel. Where would I find the label?
 
  #8  
Old 03-24-14, 07:45 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,185
The label should be inside the panel on the side.

That panel has an awful lot of dirt in it to be a new panel.
 
  #9  
Old 03-24-14, 08:02 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,284
If it is truly a 200 amp panel, the wrong lugs were installed. The fix would be to just install the proper sized lugs. The panel rating needs to be confirmed first.
 
  #10  
Old 03-24-14, 08:20 PM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 118
I bought the right lugs for the EC. He is not taking the hint. I just wanted to make sure I had my ducks in a row before I call him out on his hackery.

I guess I won't even mention since the ouside service disconnect was replaced as was the inside panel, this should now be a four wire feeder, correct?
 
  #11  
Old 03-24-14, 08:24 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,391
I think you have an issue to address with your contractor and with the inspector too, a serious issue. Was this inspected? I don't know an inspector who would have passed an installation like that.
 
  #12  
Old 03-24-14, 08:35 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,185
I guess I won't even mention since the ouside service disconnect was replaced as was the inside panel, this should now be a four wire feeder, correct?
Yes and there should be a separate grounding bar. The grounds and neutrals can no longer be in the same bar as this is considered a sub panel.

How about a larger (wider) picture.
 
  #13  
Old 03-24-14, 08:48 PM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 118
Permit is in the window, it passed rought in and yes I am still scratching my head how it passed.
 
  #14  
Old 03-24-14, 09:12 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,053
I didn't see the trimmed strands when I first posted*, maybe the inspector didn't either.

*Deleted that post.
 
  #15  
Old 03-25-14, 06:50 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,284
Many inspectors that I have come across do not really look that closely when an electrical contractor is doing the work. If a home owner is they will tend to take a closer look see. This is just my experience in the field.
 
  #16  
Old 03-26-14, 02:31 AM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,399
When I installed the new service in my previous house the inspector never even got out of his car. It wasn't until I demanded he sign the permit that he looked at anything and then he was a nit-picking fool. It took two more inspections before I got him off my back and he never did sign the silly permit.
 
  #17  
Old 03-26-14, 05:16 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,284
I would have brought the permit to him in his car.
 
  #18  
Old 03-26-14, 05:31 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
I would have brought the permit to him in his car.
With a cup of coffee. .
 
  #19  
Old 03-26-14, 06:19 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,391
I would have brought the permit to him in his car.
With a cup of coffee.
Or donuts. I took a dozen donuts to the inspector's office one morning along with a permit card to be signed. Two inspectors were standing outside as I walked up. One of them said, uh oh, what did you do wrong?
 
  #20  
Old 03-26-14, 06:25 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
Yep, works every time. One of the least-hassle jobs I remember doing was a string of KFC remodels.

BTW, what HAD you done wrong?
 
  #21  
Old 03-26-14, 06:38 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,391
One of the least-hassle jobs I remember doing was a string of KFC remodels.
Those can be hassle free if you remember your ice skates to cross the kitchen floor!

BTW, what HAD you done wrong?
Me? Nothing, nothing at all. It was the inspector who forgot to sign the card. I just took advantage of the trip to the office to take care of and chat with about 6 inspectors, besides, it all went on the expense account. Keeping a good relationship with all the inspectors is rule #1 in the contracting business.
 