I have a 220v 10/3 wire with no ground just black, red, white (2 hots and a neutral) that used to run to an old oven that has since been replaced with gas unit. I want to run this wire to a water heater so I only need 10/2 with ground. The panel box is older with neutrals and grounds sharing one bar. Can I use the neutral wire as a ground and mark it on both ends as such?
 
  #2  
Old 03-27-14, 06:31 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,935
Received 181 Upvotes on 159 Posts
It would technically be a code violation to reidentify the white as a grounding conductor. However it would work.
 
 