New basement Bathroom question

Hi, I am wiring a new bathroom in our basement ( new house ) and was wondering this, I know I have to have a 20amp circuit for the bathroom GFCI with 12/2 wire and my question is this.
Can I run the bathroom fan and light from the GFCI load side to also protect them with the GFCI or does the light and fan have to be on a separate circuit to meet code?
I have plenty of space on the panel and this is a guest bathroom that will have very little use.
I am in Edmonton Canada.

Thank you in advance for your help

Darren
 
Sponsored Links
  #2  
Old 03-31-14, 02:36 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Can I run the bathroom fan and light from the GFCI load side to also protect them with the GFCI
Yes, if the location such as within the footprint of a tub or the manufactures instructions require it but usually they are run from the line side so you are not in the dark if you trip the GFCI.
does the light and fan have to be on a separate circuit to meet code
No if this is the only bathroom on the circuit.
 
  #3  
Old 03-31-14, 03:01 PM
Member
Thread Starter
Join Date: Mar 2014
Location: Alberta Canada
Posts: 5
Received 0 Votes on 0 Posts
That is great and the line side makes sense, didn't really think of that as was thinking more of safety but as it is the only bathroom on the circuit I will do it that way.
Thank you for your help and quick, clear answer.
Darren
 
  #4  
Old 03-31-14, 04:30 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Please come back if you have any more questions.
 
  #5  
Old 03-31-14, 06:46 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,997
Received 40 Votes on 35 Posts
Rays answers are correct under the NEC in the US. The CEC may differ.
 
  #6  
Old 03-31-14, 07:16 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
OOps, didn't check location. Thanks for the catch.
 
  #7  
Old 04-01-14, 05:47 PM
Member
Thread Starter
Join Date: Mar 2014
Location: Alberta Canada
Posts: 5
Received 0 Votes on 0 Posts
Is there anyone who can tell me if this answer is still ok under CEC code, I am in Edmonton Alberta.
Thanks again..
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: