Wiring questions and my garage
Ok so I know how to wire from a fuse box/panel to add new outlets. Ive done some light research and have a couple of questions. I have a garage with no wiring but I would like to add lights and outlets. I will not need 220. I will need to use 12-2 wiring/20amp as I plan on running more than one thing at a time on occasion.
Should I run wiring from my house breaker box and right to outlets in the garage or do I need to run wiring to the garage to a separate breaker box? If I need a separate box in the garage what box/equipment would I need? Would I run the wiring from the house box the same to the garage box as if I were just adding a circuit of new outlets? If not then how?
I believe lights are supposed to be on a separate circuit and fluorescents should be wired with a certain breaker. My knowledge is limited but i listen well and learn fast.
Should I run wiring from my house breaker box and right to outlets in the garage or do I need to run wiring to the garage to a separate breaker box? If I need a separate box in the garage what box/equipment would I need? Would I run the wiring from the house box the same to the garage box as if I were just adding a circuit of new outlets? If not then how?
I believe lights are supposed to be on a separate circuit and fluorescents should be wired with a certain breaker. My knowledge is limited but i listen well and learn fast.
#2
Attached or detached garage? What loads will you have in the garage, compressor, welder, table saw, electric heater etc.
No, lights and receptacle can be on the same breaker and fluorescent don't need a special breaker.
I believe lights are supposed to be on a separate circuit and fluorescents should be wired with a certain breaker.
#3
Once you answer the questions above we can get a better idea of which way to direct you. A circuit or two may work, but a sub panel might be better.
#4
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ill be running a compressor, miter saw, grinder, hand drill, welder wired for a regular outlet not 220 and most likely florescent lights- im thinking two separate units with two bulbs each. And the garage is detached.
Last edited by borjawil; 04-03-14 at 07:48 AM.
#5
Then you will need a subpanel. It will have 240 volts available because you just don't run 120 subpanels except in special circumstances which this isn't. Because of the number of circuits I would suggest a 100 amp subpanel supplied by a 60 amp breaker using either 6-3 UF-b buried 24" or three #6 and one #10* THWN individual conductors in ¾" PVC conduit buried 18".
If you buy a main breaker panel kit it will probably be the cheapest but #6 may be too small for the main breaker so you will have to pigtail wire large enough for the main breaker. This is the route I'd go.
Some though will recommend a main lug panel with a 60 amp back fed breaker but unlike the main breaker panel kit it will probably not include any branch circuit breakers and in addition you will have to buy a 60 amp breaker.
A third option is a main lug panel and an unfused 60 amp A/C disconnect.
What ever way you go the panel will probably not come with a ground bar you will have to buy and install one plus you will need at least one ground rod at the garage.
*One #6 white, two # 6black (or one #6 red, one #6 black), and #10 green.
If you buy a main breaker panel kit it will probably be the cheapest but #6 may be too small for the main breaker so you will have to pigtail wire large enough for the main breaker. This is the route I'd go.
Some though will recommend a main lug panel with a 60 amp back fed breaker but unlike the main breaker panel kit it will probably not include any branch circuit breakers and in addition you will have to buy a 60 amp breaker.
A third option is a main lug panel and an unfused 60 amp A/C disconnect.
What ever way you go the panel will probably not come with a ground bar you will have to buy and install one plus you will need at least one ground rod at the garage.
*One #6 white, two # 6black (or one #6 red, one #6 black), and #10 green.
#6
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ok you recommended 6-3 wiring, is that because it is meant/made to be buried? You also said I could just use 3 #6 and 1 #10. Am I correct in that this is 3 separate wires at 6 gauge and 1 wire at 10 gauge(1 wire white, 2 black, and the #10 green)? Then put it in pvc/conduit to protect it underground?
What is a ground rod and how is it installed? Why would I need more than one ground rod? The ground bar is mounted inside the box for the grounding wire correct?
I am trying to do this as cheap as possible and ive notice 6-3 is quite a bit more expensive than the regular 12-2. Any cheaper options?
What is a ground rod and how is it installed? Why would I need more than one ground rod? The ground bar is mounted inside the box for the grounding wire correct?
I am trying to do this as cheap as possible and ive notice 6-3 is quite a bit more expensive than the regular 12-2. Any cheaper options?
Last edited by borjawil; 04-03-14 at 10:36 AM.
#7
ok you recommended 6-3 wiring, is that because it is meant/made to be buried?
Am I correct in that this is 3 separate wires at 6 gauge and 1 wire at 10 gauge(1 wire white, 2 black, and the #10 green)? Then put it in pvc/conduit to protect it underground?
What is a ground bar and how is it installed?

What is a ground rod and how is it installed?
Ground Bar Example, yours may vary:

Image source: Excess Supply
#8
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ok great that clears a bunch up. I have a breaker (not sure if thats what it is) that says type: br240, type: c240, 120/240v cu/ai, hacr type, 2 pole j969, e7819-t
not sure if this is something i can use?
not sure if this is something i can use?
#9
Member
Join Date: Jul 2009
Location: NYC
Posts: 285
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If you buy a main breaker panel kit it will probably be the cheapest but #6 may be too small for the main breaker so you will have to pigtail wire large enough for the main breake
Since the other breaker is protecting the run, let's say someone decides to run a 80 AMP Welder off the Sub. It it code acceptable to run it as the above quote ?
I know he's saying to splice/pigtail it, cause the 6 is too small, but can one actually do this and pass inspec ?
#10
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok so i see that in my garage theres a screwin lightbulb connector. No wire to it. Which means at one point wiring was run out there. Looked real quick around the inside (no drywall, open studs) for any wiring or signs of a previous box/wiring. Did not see anything. Not sure if that helps or indicates options?
I do have out door flood type lights that have the wiring housed in the electrical conduit pipe. Would I be able to splice in there and lead the wiring to the garage or?
Just trying to save on cost of wire. measured at about 75-80ft from my breaker box in the house
I do have out door flood type lights that have the wiring housed in the electrical conduit pipe. Would I be able to splice in there and lead the wiring to the garage or?
Just trying to save on cost of wire. measured at about 75-80ft from my breaker box in the house
#12
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Would this sub panel be ok?
Square D by Schneider Electric Homeline 100 Amp 6-Space 12-Circuit Indoor Flush Mount Main Lugs Load Center with Cover No Door-HOM612L100FCP at The Home Depot
Im guessing a 100 amp panel means it can handle up to 100 amp breaker?
Any difference between 2 pole and double pole breakers? What breaker will I need?
Square D by Schneider Electric Homeline 100 Amp 6-Space 12-Circuit Indoor Flush Mount Main Lugs Load Center with Cover No Door-HOM612L100FCP at The Home Depot
Im guessing a 100 amp panel means it can handle up to 100 amp breaker?
Any difference between 2 pole and double pole breakers? What breaker will I need?
#13
It would work but you would need to buy a 60 amp 2 pole (double pole) breaker and a hold down kit plus all the branch circuit breakers. You would have space for only ten 120 volt breakers after installing the 60 amp back feed as a disconnect. If you at later date decide to use 240 for a welder and compressor that brings it down to only 6 spaces for 120 circuits.
This is what I would use: GE PowerMark Gold 100 AMP 20-Space 20-Circuit Indoor Main Breaker Value Kit Includes Select Circuit Breakers-TM2010CCU2K at The Home Depot It already has a main breaker to use as a disconnect and includes 120 volt breakers for your circuits. Plenty of room for expansion.
This is what I would use: GE PowerMark Gold 100 AMP 20-Space 20-Circuit Indoor Main Breaker Value Kit Includes Select Circuit Breakers-TM2010CCU2K at The Home Depot It already has a main breaker to use as a disconnect and includes 120 volt breakers for your circuits. Plenty of room for expansion.
#14
Pingable asked:
No because you would be putting an 80 amp load on a 60 amp breaker. THe main breaker in the subpanel is used as a switch rated at a 100 amps max.
Since the other breaker is protecting the run, let's say someone decides to run a 80 AMP Welder off the Sub. It it code acceptable to run it as the above quote ?
#15
Originally Posted by pingable
I know he's saying to splice/pigtail it, cause the 6 is too small, but can one actually do this and pass inspec?
#16
Originally Posted by pingable
I know he's saying to splice/pigtail it, cause the 6 is too small, but can one actually do this and pass inspec?
#19
Ok so what are the differences from a main breaker box and a sub panel
Also the kit has 20amp breakers, i thought I needed a 60 amp breaker.
This is a main breaker panel. See how the feed to the panel connects to a main breaker:

This is a main lug panel. See how the feed connects directly to the lugs. You have no way to turn off the feed. If it is used as a subpanel for a detached structure you have to add some way to switch off the feed if it can have more then six 120 volt breakers.

Last edited by ray2047; 04-04-14 at 07:56 AM.
#20
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ah I see! Thanks for explaining things well. Pictures really help too. So I install/use a 60 amp breaker in my house box and connect the leads from that to the box in my garage where Ill be using 20 amp breakers for my wall sockets. Do I connect the leads from the house 60amp breaker like the second picture or would I have another 60amp in that box as well?
#21
If the subpanel is in the same structure as the service panel you do not need another breaker as a disconnect in the subpanel and can just wire to the lugs.
#22
Member
Is a panel overkill for a garage? OP stated no 240 loads, just a "regular" welder. Could he not get by with a 20 amp two-pole breaker, 12/3 UF cable, a double pole disconnect switch, and no ground rods?
#24
Since this is a detached garage PCBoss's last post doesn't apply to you.
Do I connect the leads from the house 60amp breaker like the second picture or would I have another 60amp in that box as well
- Main breaker panel as subpanel
If you use a main breaker panel as your sub the leads from the house connect to the main breaker in the subpanel. - Main lug panel as subpanel.
You would add a 60 amp double pole breaker to the panel, lock it in place with a hold down clamp, and connect your feed to that. The 60 amp breaker goes to the same place the branch circuit breakers go.
#25
Service panel? When did we add a service panel?
#26
Is a panel overkill for a garage? OP stated no 240 loads, just a "regular" welder. Could he not get by with a 20 amp two-pole breaker, 12/3 UF cable, a double pole disconnect switch, and no ground rods?
Borjawil wrote:ill be running a compressor, miter saw, grinder, hand drill, welder wired for a regular outlet not 220 and most likely florescent lights...
#27
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Money is tight and I will only be using the 120v welder which does me just fine for my project. I dont need more at this time and wont be able to afford a better welder for some time.
Also I wont be running all of these things at once. maybe two of them at once like the drill or mitersaw and the compressor.
Also I wont be running all of these things at once. maybe two of them at once like the drill or mitersaw and the compressor.
#28
Money is tight and I will only be using the 120v welder
#29
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
care to give a diagram showing the wiring for the 12-3 multiwire setup? Sorry I do better with pictures and need to understand what breakers are where and such. Thanks!
#30
Member
From http://www.garagejournal.com/forum/s...ad.php?t=61116 [ATTACH=CONFIG]29662[/ATTACH]
Disconnect is a double pole snap switch. 12/3 w/ground attaches to 20 amp double pole breaker in panel (red and black wires).
Disconnect is a double pole snap switch. 12/3 w/ground attaches to 20 amp double pole breaker in panel (red and black wires).
#31
Member
Thread Starter
Join Date: Apr 2014
Location: usa
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
still shopping around for wire. Found some a good deal on 12awg thhn wire. Would that be the same as the 12-3 wire? Would I also need a ground wire? Can I use this same 12 thhn wire for the ground? Does it need to be solid copper wire or can it be stranded?
#32
still shopping around for wire. Found some a good deal on 12awg thhn wire. Would that be the same as the 12-3 wire?
#34
The colors help to identify the function of the wires. Certain colors are reserved for grounding and grounded conductors by the code. Smaller conductors need to have the proper color insulation. Larger conductors can be identified by tape or other means.