12-4 to wire one constant hot duplex receptacle and one spilt switched recep.
Hi could I use 12-4 to have one constant hot duplex receptacle and one split switched receptacle controlled by 2 switches in the same 2 gang box? Any problems with doing this?
#2
Nope. Right as rain and legal as sunshine, so long as each box has enough volume for that many #12 conductors plus the devices.
Don't forget to remove the tab between the two hot terminals on the duplex you want to control with the two switched.
Don't forget to remove the tab between the two hot terminals on the duplex you want to control with the two switched.
#4
Member
Thread Starter
Join Date: Jul 2013
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
These with be on the same 20 amp circuit breaker. The top receptacle of the switch duplex would be switched by a 3-way switch and the bottom of the switched duplex would be switched by a single pole switch. I was going to switch both as in the example below with 12-3, but I need a constant receptacle in theses locations to comply with code. So I was going to switch the 12-3 in the example with 12-4 and have the one duplex constant hot and the other duplex be spilt and switched by the seperate switches.
#6
Member
Thread Starter
Join Date: Jul 2013
Location: USA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Some of the boxes are in foam walls with only one channel going in for one cable. Is it considered bad practice to bring some of the cables to a very large(90 cubic inches) master splice box above my drop ceiling instead of bringing cable in then out of each receptacle box. The ceiling has removeable panels to give access to the splice box.