Running NMD-90 (Romex) In PVC Raceway


  #1  
Old 04-08-14, 05:02 AM
W
Member
Thread Starter
Join Date: Mar 2008
Posts: 48
Upvotes: 0
Received 0 Upvotes on 0 Posts
Running NMD-90 (Romex) In PVC Raceway

In my finished basement I want to run a 12/2 NMD-90 for a hot water tank (about 15 Metres). I don't want to rip open the ceiling and a NMD-90 clipped on the ceiling/wall ,drywall surface won't look very nice. Am I permitted to use PVC Wiremold Raceway ? If I'm not, what other methods of conduit could I use (other than EMT) ?
Thanks
 
  #2  
Old 04-08-14, 06:44 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Water heaters are normally on 30 amp circuits requiring #10 wire. Best practice is to run individual conductors such as THHN/THWN in conduit not cable. EMT is fine inside while the EMT can serve as ground many electricians would add a green ground wire when using individual conductors. In summary EMT from the breaker box to a metal 4x4 box at the water heater with two #10 blacks and a green. Then a whip to the water heater. If the water heater is not insight of the breaker box you need a unfused disconnect at the water heater instead of a 4x4 box.*

If WH is not in sight of the breaker box a permanently installed breaker lock can be used instead of a disconnect..
 
 