Add switch to multiwire branch and question on code
#1
Member
Thread Starter
Join Date: Feb 2008
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Add switch to multiwire branch and question on code
Hello everyone,
I Have a family room that currently doesn't have any lighting, and i wanted your advice on my plan for using an existing circuit. btw, i've studied as much as i can to try to ask clear questions.

"sorry, i didnt have time to build the model to scale" ahah
I want to add a 600w dim switch to the end of one multiwire branch circuit. it currently only serves 3 duplex outlets, one of which is below where i plan to add a switch to control 8 10w pr30 LED recessed lights. i will account for 65w as max
FIRST OFF! in the diagram, the first duplex outlet BOX is a "home run" that i found by mistake (Red wire was still hot even after outlet breaker was off). the two circuit breakers i found feeding this multiwire are NOT connected with a device to flip both breakers that are on different phases> do i need to add one for code?
THis house already mixes outlets and switches, i assume that is okay for code?
i will be around 520 max at the switch, leaves around 1800 watts for 3 outlets...should be okay for dinning room?
I look forward to your feedback and questions< thanks! -travis
I Have a family room that currently doesn't have any lighting, and i wanted your advice on my plan for using an existing circuit. btw, i've studied as much as i can to try to ask clear questions.

"sorry, i didnt have time to build the model to scale" ahah

I want to add a 600w dim switch to the end of one multiwire branch circuit. it currently only serves 3 duplex outlets, one of which is below where i plan to add a switch to control 8 10w pr30 LED recessed lights. i will account for 65w as max
FIRST OFF! in the diagram, the first duplex outlet BOX is a "home run" that i found by mistake (Red wire was still hot even after outlet breaker was off). the two circuit breakers i found feeding this multiwire are NOT connected with a device to flip both breakers that are on different phases> do i need to add one for code?
THis house already mixes outlets and switches, i assume that is okay for code?
i will be around 520 max at the switch, leaves around 1800 watts for 3 outlets...should be okay for dinning room?
I look forward to your feedback and questions< thanks! -travis
#2
I want to add a 600w dim switch to the end of one multiwire branch circuit. it currently only serves 3 duplex outlets, one of which is below where i plan to add a switch to control 8 10w pr30 LED recessed lights. i will account for 65w as max
65W/fixture x 8 fixtures x 1.25 = 650W for your 8 new fixtures at 65W each (1.25 is the factor for a continuous load).
THis house already mixes outlets and switches, i assume that is okay for code?
i will be around 520 max at the switch,
leaves around 1800 watts for 3 outlets...
should be okay for dinning room?
#3
Member
You need to find another way. Wiring feeding dining room receptacles is considered to be on a Small Appliance Branch Circuit so can not feed anything but receptacles in the kitchen/dining room/pantry.
Current code is that both handles need tied together on a MWBC or use a two pole breaker.
Current code is that both handles need tied together on a MWBC or use a two pole breaker.
#4
Member
Thread Starter
Join Date: Feb 2008
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the quick replies. I was not aware that the dining room was a receptacle only branch. Looks like my only shot is to run a new circuit or look into my entry way lighting circuit in the morning. As for the switch, i will seperate the lights onto two different dimmers. Thank you!
#5
I meant to say earlier that you need to join the handles of the two breakers supplying the MWBC with a handle tie. Buy one designed to fit the breakers you have.
I would run the two 20A SABCs to the dining room if they are not already there. By blanking off the box with the receptacle in the DR that is on this circuit, or by running one of the new circuits to that location to feed the receptacle and splicing this circuit through (use a deep box), you can free up this circuit for your new lights plus giving your DR the power it needs.
Fine, if you want to. But why? Are the fixtures actually rated for more than 65W each?
Looks like my only shot is to run a new circuit or look into my entry way lighting circuit in the morning.
As for the switch, i will separate the lights onto two different dimmers>
#6
Incidentally, in a general sense, you may tap off of one hot (and the neutral) of a multiwire branch circuit and control that subcircuit using a switch. That subcircuit, with or without a switch, is not treated as a MWBC. You would have to evaluate the expected load for that subcircuit plus everything else on the half of the MWBC it was tapped off of (e.g. when planning built in light fixtures).
#7
Member
Thread Starter
Join Date: Feb 2008
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The can lights are rated at 65w each and i will look for a breaker coupler.
Now that im aware this is a small appliance circuit, connecting to this branch wont be in code. I will call an electrician to install a new circuit for the lights, as all my other circuits are pretty full
Now that im aware this is a small appliance circuit, connecting to this branch wont be in code. I will call an electrician to install a new circuit for the lights, as all my other circuits are pretty full
#8
The NEC only required that the dining receptacles be feed from one of the small appliance branch circuits, not both. Given most people's usage of a dining room I would not go to any effort to add a second 20 amp circuit to the dining room.
Prior codes only required a handle tie or two pole breaker if both hots landed on the same device yoke. The neutral did need to be pigtailed.
Prior codes only required a handle tie or two pole breaker if both hots landed on the same device yoke. The neutral did need to be pigtailed.