catv coax voltage
I was installing some coax for CATV for my parents this morning.
With the coax connected to cable box and tv but not to the splitter (line) I was getting 55VAC to ground!! With a digital multimeter.
Then I borrowed the neighbors low impendence fluke brand multimeter and it was only registering less than 1VAC.
neighbor said something about ghost voltage but in order to not look like an idiot I just agreed... what is he referring to?
With the coax connected to cable box and tv but not to the splitter (line) I was getting 55VAC to ground!! With a digital multimeter.
Then I borrowed the neighbors low impendence fluke brand multimeter and it was only registering less than 1VAC.
neighbor said something about ghost voltage but in order to not look like an idiot I just agreed... what is he referring to?
#2
Ghost voltage or actually induced voltage occurs when you have a live wire running parallel to a dead wire. A sensitive meter will show a random voltage on the dead wire that is actually induced on it from the live wire.
#3
Member
Thread Starter
Join Date: Oct 2013
Posts: 487
Upvotes: 0
Received 0 Upvotes
on
0 Posts
the "ghost" voltage and the minisicule voltage with the low impendance meter both disappeared when the surge strip with cable box and tv was turned off. So the induced voltage as you describe came from the box.
So what would be normal voltage ranges for a coax plugged into a cable box?
So what would be normal voltage ranges for a coax plugged into a cable box?
#4
There is no normal voltage. If you use an actual electricians voltage tester you won't measure anything.