Dryer causing conduit and breaker to be warm
Old 04-13-14, 11:30 AM
C
Breaker and pipes warm after dryer has been running.
Should I be concerned? This is a new installation... new wiring, new breaker, new outlet....
Old 04-13-14, 12:46 PM
ray2047's Avatar
Are you saying you put a clamp on amp meter around the conduit? That's not the way you measure amps but if your amp meter is digital the reading is probably phantom voltage.
Old 04-13-14, 12:49 PM
Tolyn Ironhand's Avatar
Received 868 Upvotes on 731 Posts
It is not uncommon for conduit and wires to get warm with a good load on them. Your dryer is drawing somewhere around 22-24 amps while running.
Grounding has nothing to do with the breaker or conduit getting warm. It is current in the wire.
Old 04-13-14, 01:40 PM
C
Thanks! You guys are great. A+
Old 04-13-14, 03:24 PM
ray2047's Avatar
Glad to help.