#14 ground wire on 30A circuit
#1
Member
Thread Starter
Join Date: Dec 2013
Posts: 236
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#14 ground wire on 30A circuit
I noticed that the electricians that ran a new circuit for my 30A dryer used a #14 as the ground. (metal conduit and has 2 hot #10, a white #10 and #14 green which is connected to the outlet). It runs about 60' to the panel.
Im thinking this is wrong and I am concerned that this is a safety hazard?
Is this something I should be complaining about?
p.s.- the bonding strap on the dryer has been removed. And a 4 wire cord/outlet is being used.
Im thinking this is wrong and I am concerned that this is a safety hazard?
Is this something I should be complaining about?
p.s.- the bonding strap on the dryer has been removed. And a 4 wire cord/outlet is being used.
#2
The metal conduit also provides grounding. Pigtail the ground wire to both the box and the receptacle using two #10 pigtails if the electrician didn't.
Last edited by ray2047; 04-13-14 at 06:47 PM.
#6
Is this what he installed?: http://www.idealindustries.com/media...um/30-3184.jpg[ATTACH=CONFIG]29938[/ATTACH]
#9
I agree with PJ it reads to me that the #14 is from the panel. I may have confused the issue by suggesting that a supplemental ground be added from the box to the receptacle so the primary ground is the conduit and the #14 from the panel just be bonded to the box. I am assuming a metal box. I wrote:
I am editing that to say use #10 to clarify.
Pigtail the ground wire to both the box and the receptacle if the electrician didn't.
#10
Member
Thread Starter
Join Date: Dec 2013
Posts: 236
Upvotes: 0
Received 0 Upvotes
on
0 Posts
To clarify--#14 from panel to outlet. No pigtail to box.
My questions:
Is this a safety hazard?
Are dryer recepticals self grounding?
Can I fix this without having to pull a #10 from panel?
Should I be complaining to the contractor about this?
My questions:
Is this a safety hazard?
Are dryer recepticals self grounding?
Can I fix this without having to pull a #10 from panel?
Should I be complaining to the contractor about this?
#11
My questions:
Is this a safety hazard?
Are dryer recepticals self grounding?
Can I fix this without having to pull a #10 from panel?
Should I be complaining to the contractor about this?
Is this a safety hazard?
Are dryer recepticals self grounding?
Can I fix this without having to pull a #10 from panel?
Should I be complaining to the contractor about this?
#12
Member
Thread Starter
Join Date: Dec 2013
Posts: 236
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks Joe. But I am still unclear... how do I fix this without 1. calling the contractor back and 2. without having to pull new wire or open up the breaker box?
Is pigtailing the #14 with a #10 connected to the box and a another #10 to the outlet code compliant?
Or is if even necessary to "correct" this?
Is pigtailing the #14 with a #10 connected to the box and a another #10 to the outlet code compliant?
Or is if even necessary to "correct" this?
#13
Is pigtailing the #14 with a #10 connected to the box and a another #10 to the outlet code compliant?
I don't see any reason why that wouldn't be code compliant.
#14
Member
Thread Starter
Join Date: Dec 2013
Posts: 236
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Is there anything I have to assure is correct before pigtailing to the box?
Either was if a fault were to occur, that #14 would see that current correct? So it would still be undersized and burn up..... The #14 connected to bus would be quicker return to voltage than the conduit system no?
Im just trying to understand why this would be an acceptable fix to pigtail instead of just using the #14 as is... afterall, the conduit is still bonded without the pigtail. Seems kind of redundant.
Either was if a fault were to occur, that #14 would see that current correct? So it would still be undersized and burn up..... The #14 connected to bus would be quicker return to voltage than the conduit system no?
Im just trying to understand why this would be an acceptable fix to pigtail instead of just using the #14 as is... afterall, the conduit is still bonded without the pigtail. Seems kind of redundant.
#15
Receptacle is not self grounding therefore there must be an adequate size ground wire to the metal box. So long as the metal conduit is continuous it is your main ground. Even if you disconnected the green at the panel and pulled it out you would still have a safe code compliant ground so long as the conduit is continuous and a #10 pigtail is used.
Check that the conduit is continuous with no missing sections and is fastened to the panel and Jbox. Pull the cover from the breaker box and the Jbox and post a clear picture of how the conduit is terminated at both ends. http://www.doityourself.com/forum/li...-pictures.html
No reason that would be true.
The 14 is not adequate to ground the receptacle and the receptacle isn't self grounding so you need the #10 pigtail to ground the receptacle.
Is there anything I have to assure is correct before pigtailing to the box?
The #14 connected to bus would be quicker return to voltage than the conduit system no?
Im just trying to understand why this would be an acceptable fix to pigtail instead of just using the #14 as is
#18
Member
Thread Starter
Join Date: Dec 2013
Posts: 236
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It doesn't matter but can't hurt.
#19
Member
Join Date: Nov 2013
Posts: 213
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Even if you had #10 between panel and dryer outlet it still would not be correct I don't think.
Doesn't that #10 (or your erroneous #14) have to be bonded/jumpered to the metal box as well? Maybe a pro can chime in on that aspect..... that might negate the use of that #14 all together.
im all ears since I am buying a new dryer this week and plan on installing it myself.
Doesn't that #10 (or your erroneous #14) have to be bonded/jumpered to the metal box as well? Maybe a pro can chime in on that aspect..... that might negate the use of that #14 all together.
im all ears since I am buying a new dryer this week and plan on installing it myself.
#21
Member
Thread Starter
Join Date: Dec 2013
Posts: 236
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My opinion is the #14 is not needed IF there is a #10 pigtail from the grounded metal box to the receptacle.
Wifey is asking to do the laundry and I am not sure what to tell her!!
#23
If the pigtail is only in the box with the receptacle just remove it from the ground screw and add the #10 between the box and the receptacle.
#25
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 1,983
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The NEC permits a "combination" of Equipment Grounding Conductors , and your "combination" is the metallic surface of the EMT and a ( bare) #14 copper wire .
Fasten a terminal "lug" to the metallic surface of the outlet-box and use the lug as a terminal connection for the #14 wire, and a #10 "Jumper" wire that connects the Grounding terminal of the receptacle to the metallic surface of the box and the #14 Grounding Conductor.
Fasten a terminal "lug" to the metallic surface of the outlet-box and use the lug as a terminal connection for the #14 wire, and a #10 "Jumper" wire that connects the Grounding terminal of the receptacle to the metallic surface of the box and the #14 Grounding Conductor.
#26
So what do I do with the bare #14 then that would be connected to the busbar in the panel? Leave it tucked in the back of the box?