How would you label the outlets?

Theres a junction in the ceiling that leads to the outlets, perhaps it a good idea to mark it.... not sure of the wording I should use to make it look neat.

The only thing that makes it look different than other outlets in my house is that I use grey outlets, used pass Seymour (instead of Leviton) and I used 20A outlets instead of 15.
 
Sponsored Links
  #42  
Old 04-23-14, 10:04 AM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Received 0 Votes on 0 Posts
I'd label it something along the lines of "Emergency Power".
 
  #43  
Old 04-23-14, 10:37 AM
Banned. Rule And/Or Policy Violation
Join Date: Jan 2010
Location: KS
Posts: 1,896
Received 0 Votes on 0 Posts
No, because that implies there is a backup power source connected to it.

Mark it "SDS: Generator Inlet"..

SDS = Separately Derived Source. It's a term any inspector should be familiar with.
 
  #44  
Old 04-23-14, 01:32 PM
Member
Thread Starter
Join Date: Oct 2013
Posts: 592
Received 0 Votes on 0 Posts
Got it, thanks for the help.

I labeled the junction SDS-GENERATOR INLET and labeled the outlet boxes 20A-GENERATOR

Fired it up this afternoon and I am getting my power in the basement albeit high (129 volts AC- no load) hopefully I don't have to mess with the governor here.
 
  #45  
Old 04-25-14, 11:45 AM
Member
Thread Starter
Join Date: Oct 2013
Posts: 592
Received 0 Votes on 0 Posts
I was telling a coworker about this installation and he said that I made a mistake with using #12 off the 30A twist lock... that it should be #10 and that the 240 twist lock is protected by a 30A breaker.

Is that the case?
 
  #46  
Old 04-25-14, 12:09 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,996
Received 39 Votes on 34 Posts
Number 10 should be used for 30 amp circuits.

Regular receptacle circuits are limited to 20 amps maximum.
 
  #47  
Old 04-25-14, 01:13 PM
Banned. Rule And/Or Policy Violation
Join Date: Jan 2010
Location: KS
Posts: 1,896
Received 0 Votes on 0 Posts
No, your 5000w generator does not have a 30A breaker. On most small (under 7500W) generators the twist-lock receptacle is fed off the same 20A breakers as the 120V receptacles. Only on larger generators will they be protected by a separate 30A breaker.
 
  #48  
Old 04-25-14, 01:46 PM
Member
Thread Starter
Join Date: Oct 2013
Posts: 592
Received 0 Votes on 0 Posts
Number 10 should be used for 30 amp circuits.

Regular receptacle circuits are limited to 20 amps maximum.
Yes, we know this. But as Jerseymatt points out, there is no 30A circuit (despite the 30A outlet) on a 5500 watt generator.
 
  #49  
Old 04-25-14, 06:13 PM
Banned. Rule And/Or Policy Violation
Join Date: Jan 2010
Location: KS
Posts: 1,896
Received 0 Votes on 0 Posts
Once again this is a special application, so many NEC rules don't apply. TECHNICALLY, according to Table 310.16 the actual ampacity of #12 wire is either 25 or 30A, depending on the wire's insulation rating. NEC 240.4(D) is what limits the breaker size on branch circuits to 15A on #14, 20A on #12, and 30A on #10- which trumps Table 310.16. Since this is not a branch circuit, NEC 240.4(D) does not apply. So if you pulled THHN/THWN-2 conductors with 90C insulation (which it most likely is), it can safely carry 30A.
 

Last edited by JerseyMatt; 04-25-14 at 06:28 PM.
  #50  
Old 04-25-14, 11:36 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Received 0 Votes on 0 Posts
For future reference, here's what I've come across in the portable generators I've installed, seen, or otherwise used.

4,000W and below: 15A 240V or 30A 120V.
4500W-5500W: 20A 240V
6,000W and the like: 25A 240V
7,000W-8,000W 30A 240V
10,000W 40A 240V
12,000W 50A 240V
15,000W 60A 240V
Above 15,000W varies greatly depending on manufacturer and purpose.

Keep in mind most portable generators are designed for a power factor of 1, and loads such as motors, tv's, computers, HID, CFL and LED lights, cell phone chargers, etc. Use more VA (volt*amp) than watts and in which case you need to use the VA for calculating your load.
 
  #51  
Old 04-26-14, 08:19 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,011
Received 39 Votes on 34 Posts
No I am not an electrician but I know the generators that have a 120 only switch do funny things with the wiring.

Often I believe is that the 2 breakers that are wired for the regular outlets are then both put into parallel for the 120v only outlet. Its the only way these can be wired from the two windings in the gen.

Example: If the gen has two 15 amp breakers for the outlets they then become wired in parallel for the 120v outlet making it 30amp...

Now typically I am not sure if you will see a 120v only outlet on a gen over 5000watts.

And I believe the breakers are often used in parralel for the 240/120 twist lock also...
 
  #52  
Old 04-26-14, 09:41 AM
Banned. Rule And/Or Policy Violation
Join Date: Jan 2010
Location: KS
Posts: 1,896
Received 0 Votes on 0 Posts
The 120/240 switch only affects a 30A/120V 3 pin locking receptacle if present on the generator. Basically its for running a camper/RV. It disables the 240V 4 pin twist-lock because in 120V mode there aren't two separate windings to make the two hot legs anymore.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: