Combo Washer Dryer wiring help needed.

I found a good deal on a stacked combo washer. Maytag se1000. This is the old type that will last a lifetime. It has the tried and true helical drive! Im done with junk front loaders.

Anyways I'm moving the laundry facilities upstairs to an unused closet. I have all my plumbing run with out any problem. Now I have to run the electric. The Dryer part of the machine runs off 240 and the washer part runs off 120. I know code says I can split at the receptacle and pull my 120 off one leg. Can I wire the 120 to pull off one of the 240 legs inside the machine? I have a dedicated 30 amp 240 breaker for my dryer and I have 10-3 with ground for the dryer. I know a lot of the washer dryer stacked units only require 120 or 240. Mine requires both right now.
 
Sponsored Links
  #2  
Old 05-06-14, 09:30 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,662
I know code says I can split at the receptacle and pull my 120 off one leg.
Can you site section of NEC? A 120 volt receptacle can not be fused for more that a 20 amps. A dryer typically is 30 amps.
 
  #3  
Old 05-06-14, 05:07 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
I have a dedicated 30 amp 240 breaker for my dryer and I have 10-3 with ground for the dryer.
Assuming your are correct and the dryer needs 240 volts, you wouldn't need 10-3 NM cable, but just 10-2 NM cable.

How many power cords come from the washer/dryer combo? What are the configurations of the plugs/plug?
 
  #4  
Old 05-06-14, 08:13 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,494
That is really strange. That model is made in several different variations. Single power cord or dual. My sister has the single 240vac model that requires 30A 240vac and a ground (3 wire).
 
  #5  
Old 05-07-14, 05:06 AM
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 57
Ray: I ment "cant". Code says you cant split at the receptacle. Amazing what one missing "t" can do to a sentence.

CausalJoe: The Washer/Dryer has 2 plugs coming from it. One is 240 three prong. the other is regular 120 three prong. Since I'm moving the dryer wiring i have to upgrade to 10-3 with ground to meet code. I will then wire the dryer with a new plug to keep up with code.

PJmax: Is it the same washer dryer combo. I think back when they were sold they could be configured how every you would like. If you wanted one plug they would just wire the 120 plug to a leg of the 240 inside the machine, I believe. I cant find any manuals with install information for this machine. I know most modern machines come configured that way.
 
  #6  
Old 05-07-14, 06:35 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
The Washer/Dryer has 2 plugs coming from it. One is 240 three prong. the other is regular 120 three prong.
240 volt 3 prong meaning 2 hots and 1 ground?

Since I'm moving the dryer wiring i have to upgrade to 10-3 with ground to meet code.
I'd next check the electrical data plate on the dryer. If it says 240 volt you still don't need 10-3 NM cable to meet the dryer's requirement or to meet code and can use 10-2 NM cable. That being said, if it is possible that someone in the future may want to use a typical stand-alone electric dryer at this new laundry location, I'd go ahead and install the 10-3 NM cable and just not use the neutral at this time.

The Washer/Dryer has 2 plugs coming from it.
I'd also install a new dedicated 20 amp, 120 volt circuit to this new laundry location.
 
  #7  
Old 05-07-14, 11:15 AM
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 57
2 hots, one neutral that is tied to ground. Code states that if you move wiring you have to update it to code. The dryer doesnt require 10-3 but code says any new or moved dryer receptacles need to be run with 10-3. Its an old washer and dryer and im hoping it will last a while. They are the washers that put the maytag repair man out of business. With that said its 25-30 years old so who knows how long it will last. When it does go I may upgrade to a different dryer at the location and I would hate to have to replace the new wire i just put in. Looks like I'll just run a 120 20 amp circuit. Seems like a shame when 240 is there and this model seems to have a one plug option.
 
  #8  
Old 05-08-14, 07:08 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
2 hots, one neutral that is tied to ground.
2 hots and 1 neutral is for a 120/240 volt circuit, not a 240 volt circuit. If your dryer part of the combo requires a neutral, it isn't a 240 volt appliance, but a 120/240 volt appliance. A 240 volt appliance requires 2 hots and 1 ground.

The dryer doesnt require 10-3 but code says any new or moved dryer receptacles need to be run with 10-3.
If a neutral is required for the dryer to operate, it does require 10-3 NM cable because it's a 120/240 volt appliance. Older 120/240 volt dryer circuits did the grounding through the insulated neutral.

Looks like I'll just run a 120 20 amp circuit. Seems like a shame when 240 is there and this model seems to have a one plug option.
Yes, you definitely need the 20 amp, 120 volt circuit for the washer and a proper 120/240 volt 4-wire circuit with both an insulated neutral and separate ground terminated in a proper 4-wire receptacle (14-30 R). You'll also need to disconnect the bond between ground and neutral in the dryer and install a 4-wire cord/plug (14-30P) to match the receptacle.
 