Marking Single Phase Wiring
I know you can't mark/id anything smaller than 4AWG when phasing..
However, for single phasing, can I just buy a spool of 500 feet....and mark ID red and white , on 8 AWG wire ?
However, for single phasing, can I just buy a spool of 500 feet....and mark ID red and white , on 8 AWG wire ?
#4
“200.6 Means of Identifying Grounded Conductors.
(A) Sizes 6 AWG or Smaller. An insulated grounded conductor of 6 AWG or smaller shall be identified by one of the following means:
(1)
A continuous white outer finish.
(2)
A continuous gray outer finish.
(3)
Three continuous white or gray stripes along the conductor's entire length on other than green insulation.
Excerpt From: National Fire Protection Association (NFPA). “NFPA 70®, National Electrical Code® (NEC®), 2014 Edition.” NFPA. iBooks.
This material may be protected
(A) Sizes 6 AWG or Smaller. An insulated grounded conductor of 6 AWG or smaller shall be identified by one of the following means:
(1)
A continuous white outer finish.
(2)
A continuous gray outer finish.
(3)
Three continuous white or gray stripes along the conductor's entire length on other than green insulation.
Excerpt From: National Fire Protection Association (NFPA). “NFPA 70®, National Electrical Code® (NEC®), 2014 Edition.” NFPA. iBooks.
This material may be protected
#6
for single phasing, can I just buy a spool of 500 feet....and mark ID red and white , on 8 AWG wire ?
#7
Best to ask your LOCAL inspector. Some inspectors will absolutely demand that you use different colors while some will allow a HOMEOWNER to re-identify smaller conductors. No inspector will allow a professional electrician to re-identify smaller than #4 conductors.
The reason for the break at #4 conductors is that the code-making panel decided that it was not a hardship to require an electrical contractor to use the proper colors since they would be able to use the remainder of the spool on a different job and also because wire of #4 and larger is generally not available with different insulation colors. It IS important to re-identify the conductors at ALL points of access such as conduit bodies and pull boxes regardless of any actual connections in these areas.
The reason for the break at #4 conductors is that the code-making panel decided that it was not a hardship to require an electrical contractor to use the proper colors since they would be able to use the remainder of the spool on a different job and also because wire of #4 and larger is generally not available with different insulation colors. It IS important to re-identify the conductors at ALL points of access such as conduit bodies and pull boxes regardless of any actual connections in these areas.