2 or 3 Wire Romex for Central Air Condenser?

Hi,

I currently have the walls open around my main box for some renovations I am doing and while the walls are open, I want to pre-run wiring for adding central air in the future.

For the condenser, I am planning on running #8 Romex but I am not clear if central air condensers usually need 2 or 3 wire Romex (e.g., 8/2 or 8/3). Any insight you have would be very appreciated.

Thanks,
Matt
 
  #2  
Old 05-07-14, 06:48 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
They are 240 so they need 2 conductor +ground. If there isn't a receptacle within six feet of the location you may also want to run 12-2 for a 120 volt maintenance receptacle.
 
  #3  
Old 05-07-14, 07:39 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
# 8 is way overkill. You might be able to run #12 or even #14.
 
  #4  
Old 05-08-14, 07:22 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,787
Received 173 Upvotes on 156 Posts
Not having any idea of the size of the house or size of any future new A-C unit, I'd be hesitant to run anything smaller than 10-2 /G NM cable
 
  #5  
Old 05-08-14, 08:06 AM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,272
Upvotes: 0
Received 1 Upvote on 1 Post
From my experience you can get away with as small as 14-3 for the inside unit and usually 10-3 is good for the outside unit. I've run as large as 6-3 for the outside unit, and dual 6-3 for the inside unit because the inside unit for heat strips. You really need to know the requirements of the air handler and outside unit before running your wiring. You can also get away most likely with */2 cable, too, but I usually run */3 cable in case it would ever be needed.
 
  #6  
Old 05-08-14, 10:43 AM
M
Member
Thread Starter
Join Date: Nov 2013
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the tips guys.

House is 2 stories and ~2700 sq ft. I am thinking #8 wire for the compressor to be better safe than sorry. At this point, I don't have any idea of the actual compressor I would end up getting in the future and I really don't want to re-open up the walls at that time.

Matt
 
  #7  
Old 05-09-14, 10:38 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,787
Received 173 Upvotes on 156 Posts
House is 2 stories and ~2700 sq ft. I am thinking #8 wire for the compressor to be better safe than sorry.
You could do that as long as you won't need two condensing units.
 
  #8  
Old 05-09-14, 05:59 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,758
Received 676 Upvotes on 573 Posts
While you have the walls open you should also run a 120 volt line with your A/C line. Code requires a GFCI protected receptacle within 25' of A/C equipment.
 
 