Question Lighting Circuit - 3 feeds from 2 gang switch box

Refer to my attached image (diagram):

I'm planning electrical for my kitchen remodel. I have an existing lighting circuit, 20A with 12-2 wiring from the breaker box on the far corner of my house to an accessible junction box near my kitchen. From that junction box I'd like to run a feed to the wall switch location near my sink. From there, I need 3 things:

a switched line for can lights above the sink
a switched line for under cabinet lighting
an unswitched line for in-cabinet puck lighting

Can I run 12-2 from the basement j-box to the 2-gang switch box and feed all three out from there, or do I need to handle in a different way?

Any advice is appreciated. Thank you,

Brian
 
Attached Images  

Last edited by bmears; 05-08-14 at 03:28 PM.
Sponsored Links
  #2  
Old 05-08-14, 03:23 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,050
I have an existing lighting circuit, 20A with 12-2 wiring from the breaker box... Can I run 14-2 from the basement j-box to the 2-gang switch box
Only if you change the breaker to 15 amps but best practice is to not use mixed wire sizes. Someone later might see the #12 and change the breaker to 20a not realizing there was #14 mixed in.
 
  #3  
Old 05-08-14, 03:29 PM
Member
Thread Starter
Join Date: Oct 2001
Location: USA
Posts: 146
Nuts - that was a typo (fixed now). I would be running 12-2 from the j-box to the switch box (and beyond), NOT 14-2. Everything would be #12 wire. Knowing that, can it be done as described?
 
  #4  
Old 05-08-14, 03:34 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,050
Yes. Just remember under 2011 NEC all switch boxes not connected by conduit must have a neutral even if not used. So simplest is to bring power to the switch then the light but your diagram gets that right so no problem.
 
  #5  
Old 05-08-14, 04:01 PM
Member
Thread Starter
Join Date: Oct 2001
Location: USA
Posts: 146
Awesome. I thought it was that straightforward but haven't tackled a large wiring project since 2007ish. Thanks again for the help!
 