I need to run 3 outlets in my unfinished basement, I will tap into an existing line with only one outlet on it and run towards my intended direction. The layout plan is in the form of a "T" so it will be more practical to BRANCH rather than CHAIN the outlets. Is it acceptable to run the power wire to a junction box and pigtail all the wires (4 wire pigtail) and than run the 3 branch lines out from there?

thank you
 
  #2  
Old 05-15-14, 09:00 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
NO! Absolutely not! Never!

Okay, I lied, what you propose is perfectly fine.
 
  #3  
Old 05-15-14, 09:09 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,679
Received 50 Votes on 45 Posts
With daisy-chaining you don't have as many issues with box fill. Branching out (hub-and-spoke) methods usually overload a standard switch/receptacle box. If your junction box is a 1900 (4x4) you should be good, though.
 
  #4  
Old 05-15-14, 09:11 PM
D
Member
Thread Starter
Join Date: Nov 2011
Location: usa
Posts: 219
Received 0 Votes on 0 Posts
you made me nervous for a moment!

i ask because adhering to a traditional "chaining" pattern will be a waste of unnecessary wire given the layout

thanks
 
  #5  
Old 05-15-14, 09:31 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,452
Received 131 Votes on 120 Posts
Example of box fill (U.S.):

One 12/2 power cable and three (12/2) branches continuing: 8 conductors equals 8 points. One receptacle unit (duplex or round single) in the box, 2 points. All the ground wires (equipment grounding conductors) 1 point. Any or all the cable clamps or fingers protruding into the box, 1 point. Pigtails (short lengths wholly within the box) e.g. to reach the receptacle, 0 points each. Wire nuts, 0 points each. Total of 12 points, 2-1/4 cubic inches per point equals a minimum box size of 27 ci.
 
  #6  
Old 05-16-14, 08:01 PM
D
Member
Thread Starter
Join Date: Nov 2011
Location: usa
Posts: 219
Received 0 Votes on 0 Posts
so a 4"x4"x2.25" square box = 36ci correct?
my junction box would be stand alone, hub plus 3 spokes (4 wire pigtail)
incidentally what is the maximum number of advisable wires in a pigtail?
 
  #7  
Old 05-16-14, 08:45 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,252
Received 113 Votes on 98 Posts
The pigtaoils are limited by the size of the wire nut and wire sizes.
 
 