Synchronize generator equipments?
if i have 313KVA diesel gen. and i want to synchronize with another generator, what equipmtent do i need??? it uses synchronize panel.
items:
what generator rating?
sync panel?
automatic transfer switch operated
i dont know the other one that is connected to the generator
Thanks
items:
sync panel?
Thanks
Welcome to the forums.
Many difficult questions. The gennys must be speed synched as well as phase synched.
Since your first genny is a Cummins... I would make sure the second one is from the same company. If you use gennys from different manufacturers you run the risk of high circulating currents in the windings. The capacity of the second genny is the difference between your 313KVA and the total wattage you need. You'll need to check with Cummins to make sure their gennys are set up for parallel operation and the governors have droop mode which is a method of allowing two generators to operate in parallel and share load.
I would check directly with the tech services at Cummins for exact requirements.