Putting in baseboard heating. What gauge wire?

I'll be putting in one 8 ft and two 4 ft heating elements. What do I need for wire gauge and circuit? I've got to add a circuit to my panel. The length of wire from the panel will be about 100 feet to the farthest element. Also, do I need a wire for each element or can I run a continuous wire to each. I'm believe the elements will be 240. Thanks!
 
Sponsored Links
  #2  
Old 05-21-14, 10:19 AM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
Received 1 Vote on 1 Post
Assuming the 8' is 2000 watts, and the 4' are 1000 each, #12 on a 2 pole 20 amp breaker should be fine.

If you use the 80% rule for continuous load, it would put you .66% over but, I wouldn't sweat it.

Yes, one continuous circuit daisy chained.
 
  #3  
Old 05-21-14, 03:24 PM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
Received 1 Vote on 1 Post
I meant .66 amps not %
 