Putting in baseboard heating. What gauge wire?
#1
Member
Thread Starter
Join Date: Oct 2007
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Putting in baseboard heating. What gauge wire?
I'll be putting in one 8 ft and two 4 ft heating elements. What do I need for wire gauge and circuit? I've got to add a circuit to my panel. The length of wire from the panel will be about 100 feet to the farthest element. Also, do I need a wire for each element or can I run a continuous wire to each. I'm believe the elements will be 240. Thanks!
#2
Assuming the 8' is 2000 watts, and the 4' are 1000 each, #12 on a 2 pole 20 amp breaker should be fine.
If you use the 80% rule for continuous load, it would put you .66% over but, I wouldn't sweat it.
Yes, one continuous circuit daisy chained.
If you use the 80% rule for continuous load, it would put you .66% over but, I wouldn't sweat it.
Yes, one continuous circuit daisy chained.