Is my 100A sufficient?

I would like to add two, 20A 120 circuits to my system. But I wanted to be sure my 100A is sufficient.

2000 SQ FT' ranch.

100A main
with 16 circuits including
gas furnace
25A air conditioner
30A electric dryer
a 40A 240 for garage subpanel that has 2 20A circuits-- only load on it is the GDO.
20A laundry
2 small appliance circuits for kitchen
Dishwasher 20A
Sump Pump 20A
6 15A circuits for rooms.

What other information is necessary for an accurate measurement?
How much can I safely add to my panel?
 
Sponsored Links
  #2  
Old 05-23-14, 06:07 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
I would like to add two, 20A 120 circuits to my system. But I wanted to be sure my 100A is sufficient.
It's probably adequate, but approaching marginal. Have you done a load calculation? I'd do the calculation and then also check the actual current draw on the service when both A-C and electric dryer are running during a typical warm day.
 
  #3  
Old 05-23-14, 09:39 AM
Member
Thread Starter
Join Date: Dec 2013
Posts: 284
Would you be so kind to explain how to do a load calculation or point me in the direction of a calculator or some directions? Thank you.
 
  #4  
Old 05-23-14, 10:43 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,643
  #5  
Old 05-23-14, 12:07 PM
Member
Thread Starter
Join Date: Dec 2013
Posts: 284
Thanks Ray. I tried using the calculator you suggested but I am uncertain if what I computed was correct. The VA vs. A etc threw me off.

I think I was getting 69A. That kind of has me concerned? I probably shouldn't be adding circuits in this case? I want to have one circuit for water heater fan and another circuit for general use. Is there a percentage of 100a your supposed to stay at for that size service?

I also noticed on the calc they don't ask about lighting and they don't ask about electronics.
 
  #6  
Old 05-23-14, 12:16 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,643
I listed two calculators. Try both and compare. A is amps the appliance draws. VA is volts X amps. Watts and VA are roughly the same.
 
  #7  
Old 05-23-14, 12:38 PM
Member
Thread Starter
Join Date: Dec 2013
Posts: 284
So actually creeping up on 80A for a 100A service is a bad thing?

ps one of those calculators, the mike holt one, there is a charge$$
 
  #8  
Old 05-23-14, 01:47 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,354
The lighting is covered under the 3 va per square foot.

The fan will use almost nothing. The general use receptacles will only have a load when you are using something.
 
  #9  
Old 05-24-14, 09:16 AM
Member
Join Date: Jan 2014
Location: USA
Posts: 699
100 amp service is kind of skimpy for a 2000 sq ft house , with gas heat and gas cooking . However 25 amp A/C is a little smaller than I am use to seeing .

100 amp main circuit breaker ?

GDO - garage door opener ? Pulls almost nothing , except when you are opening or closing the garage door .

Do you presently see the lights flicker when the dryer or the A/C kick on ? ( Hint , run the dryer at night when the A/C is running less . )

Sump pump ? You have a basement ? Again , it pulls nothing , except when it is running .

Just a long distance guess , if you never see the lights dim , you can probably get buy with the 2 new circuits . You have 2 available spaces in the loadcenter ?

God bless
Wyr
 
  #10  
Old 05-24-14, 03:05 PM
Member
Thread Starter
Join Date: Dec 2013
Posts: 284
Actually its 1400 sq ft.

So essentially its a 30A dryer. 25A AC. 1/2HP sump. 2 small appliance circuits. 1 laundry circuit.

So when approaching 70-80 is it not a good idea to push it further?

I have 5 available slots in my 24 slot panel.
 
  #11  
Old 05-24-14, 04:04 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,354
I think you will not have an issue adding those circuits. Rarely would your service ever be using that much.
 
  #12  
Old 05-25-14, 05:03 AM
Member
Join Date: Jan 2014
Location: USA
Posts: 699
You have 5 spaces in the loadcenter ? 1" spaces or 1/2" spaces ?

I recommend using 1" Circuit Breakers . I hate 1/2" CB's and only use them when I have to .

God bless
Wyr
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
'