Is the Leviton 5643 not self grounding?


  #1  
Old 05-23-14, 02:17 PM
D
Member
Thread Starter
Join Date: Jul 2005
Location: Chicago land
Posts: 644
Received 1 Upvote on 1 Post
Is the Leviton 5643 not self grounding?

I purchased a Leviton 5643 combination 3-way switch.

5643-I > Decora<sup>®</sup> Combination Devices > Combination Devices > Electrical Wiring Devices > Products from Leviton Electrical and Electronic Products


It does not have a copper spring on the front. Therefore, do I have to assume that this device is not self grounding? Will it require a ground wire?
 
  #2  
Old 05-23-14, 03:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
As an electrician I always run a ground wire to the device.

In the description it says grounding. I don't know exactly what that means though.
 
  #3  
Old 05-23-14, 03:19 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,756
Received 675 Upvotes on 573 Posts
Per NEC, a switch attached to a grounded metal box is considered grounded. Otherwise you will need to attach a ground wire to the switch.

"Grounded/grounding" just means there is a ground screw and a metal yoke.
 
  #4  
Old 05-23-14, 05:28 PM
D
Member
Thread Starter
Join Date: Jul 2005
Location: Chicago land
Posts: 644
Received 1 Upvote on 1 Post
So, what is the purpose of the copper spring that some switches/devices have when it is not required for self grounding?
 
  #5  
Old 05-23-14, 10:59 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,272
Upvotes: 0
Received 1 Upvote on 1 Post

So, what is the purpose of the copper spring that some switches/devices have when it is not required for self grounding?
To make a better ground connection. I've seen devices made by Eagle in the 1990's where that screw is actually green.
 
  #6  
Old 05-24-14, 04:54 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,471
Received 83 Upvotes on 75 Posts
Code is complicated and sometimes doesn't seem to make sense.

Spring on switch really doesn't do anything for code requirements. For receptacles the spring is required for self-grounding in metal box. For surface mounted metal boxes the spring is not required but you need to either remove one of the insulating washers on the screws or have the receptacle attached to a metal cover.
 
  #7  
Old 05-25-14, 07:02 AM
D
Member
Thread Starter
Join Date: Jul 2005
Location: Chicago land
Posts: 644
Received 1 Upvote on 1 Post
Thanks.

In most cases it seems the ground happens only through the mounting screw. Most of the time the switch/receptacle is not flush with the metal box as the drywall always seems to stick out a bit.
 
  #8  
Old 05-25-14, 07:50 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,756
Received 675 Upvotes on 573 Posts
That is correct. The yoke does not need to be in contact with the metal box to have a grounding path. The screw attached to the box, and in contact with the yoke, is the grounding path. Code allows up to 1/4" gap between the box and the wall finish.
 
 