Installing longer cord to pool pump motor


  #1  
Old 05-27-14, 10:38 AM
J
Member
Thread Starter
Join Date: May 2014
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Installing longer cord to pool pump motor

All - I'm replacing the power cord on the pool pump motor in order for me to reach a dedicated outdoor outlet. The existing cord is 6' long and is labeled as a 3/C 18 AWG SJTW (300V / 105 degree C) VW-1 FT1 FT2.

I want to replace it with a substantially longer cord (maybe 30 feet). Am I able to use the same size cord (only longer) or do I need to go with a higher gauge? I'm pretty much a newbie so please be gentle. Thanks.
 
  #2  
Old 05-27-14, 11:53 AM
J
Member
Thread Starter
Join Date: May 2014
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Why is that? Is there a hazard associated with a longer power cord?
 
  #3  
Old 05-27-14, 01:38 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
After researching my answers I have deleted them. I think though putting a receptacle closer makes more sense.
 
  #4  
Old 05-27-14, 02:35 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,970
Received 194 Upvotes on 170 Posts
From the 2011 NEC.

(1) Circulation and Sanitation System, Location. Receptacles
that provide power for water-pump motors or for other
loads directly related to the circulation and sanitation system
shall be located at least 3.0 m (10 ft) from the inside walls of
the pool, or not less than 1.83 m (6 ft) from the inside walls of
the pool if they meet all of the following conditions:
(1) Consist of single receptacles
(2) Employ a locking configuration
(3) Are of the grounding type
(4) Have GFCI protection
(2) Other Receptacles, Location. Other receptacles shall
be not less than 1.83 m (6 ft) from the inside walls of a pool.
(3) Dwelling Unit(s). Where a permanently installed pool is
installed at a dwelling unit(s), no fewer than one 125-volt, 15-
or 20-ampere receptacle on a general-purpose branch circuit
shall be located not less than 1.83 m (6 ft) from, and not more
than 6.0 m (20 ft) from, the inside wall of the pool. This
receptacle shall be located not more than 2.0 m (6 ft 6 in.)
above the floor, platform, or grade level serving the pool.
 
 