1 awg aluminum for a 200amp service


  #1  
Old 05-28-14, 01:00 PM
H
Member
Thread Starter
Join Date: May 2014
Location: Canada
Posts: 1
Received 0 Votes on 0 Posts
1 awg aluminum for a 200amp service

Can 1 awg direct burial aluminum wire be used for a 200amp service at 65 meters in length? My electrician told me it would be okay so long as it is not encased in conduit so as to reduce heat build up. However, there is conduit from the footing to the meter base. Currently the electrical code in Canada states that you can have 135amp service with aluminum 1awg encased in conduit.

I just want to make sure that this service is not compromised.

Thanks
 
  #2  
Old 05-28-14, 03:24 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: United States
Posts: 5,020
Received 90 Votes on 85 Posts
If you plan on using USE and Al. According to the 2014 NEC the conductor size should be 250 kcmil.
Geo
 
  #3  
Old 05-28-14, 03:29 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,251
Received 112 Votes on 97 Posts
#1 AL is not large enough under the NEC, I doubt that it would meet the CEC due to the similar requirements between the two codes.
 
  #4  
Old 06-02-14, 05:21 PM
spark4short's Avatar
Member
Join Date: Jun 2014
Location: usa
Posts: 5
Received 0 Votes on 0 Posts
wire size

U need to get another electrician before he causes some damage. Call building deparment if necessary. they always glad to help. Always put wire in a conduit in case of future problems.3/0 copper or 4/0 aluminum is minimum for 200 amp service on a residence.
 
  #5  
Old 06-03-14, 05:58 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,815
Received 105 Votes on 93 Posts
3/0 copper or 4/0 aluminum is minimum for 200 amp service on a residence.
The NEC allows either 2/0 copper or 4/0 aluminum for a residential 200 amp service.
 
 