Don't Understand Old Overhead Light Wiring


  #1  
Old 05-28-14, 06:03 PM
R
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 52
Upvotes: 0
Received 0 Upvotes on 0 Posts
Don't Understand Old Overhead Light Wiring

I am installing a new overhead light fixture in my 1927 home. I do not understand how the wiring works, but it does work. All I know is shown in the attached drawing. The light works if attached as shown with the two wires being interchangeable (I don't know which would be neutral, as both connections are to a black wire). Is this safe?
 
Attached Images  
  #2  
Old 05-28-14, 06:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,740 Upvotes on 3,356 Posts
Your light switch is a switch leg. You have it shown as switching the neutral which is incorrect. It should be switching the hot wire.

Name:  light_wiring.jpg
Views: 1050
Size:  33.2 KB
 
  #3  
Old 05-28-14, 06:37 PM
R
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 52
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks once again PJMax for your quick and thorough response. I'll rewire as you suggest--probably tomorrow--and report back.

Thanks.
 
  #4  
Old 05-28-14, 06:43 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,740 Upvotes on 3,356 Posts
You turn the light off to your fixture to service it. Since you turned the switch off and it's no longer working you assume it's dead but it is still live since you are switching the neutral instead of the hot.

Years ago it seemed to be popular to switch either wire.
 
  #5  
Old 05-28-14, 06:53 PM
R
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 52
Upvotes: 0
Received 0 Upvotes on 0 Posts
I figured that and edited my post before realizing you had already responded.

I've always turned lights off at the circuit breaker before working on them even though I thought it unnecessary. Now I see there is good reason to do that.
 
  #6  
Old 05-29-14, 06:56 PM
R
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 52
Upvotes: 0
Received 0 Upvotes on 0 Posts
I rewired as PJMax suggested and all is well. Thanks again.
 
  #7  
Old 05-29-14, 07:07 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,740 Upvotes on 3,356 Posts
You're welcome.... good move too
 
 