Number of wires in plastic pipe

Can I safely run 3 (240 black, red and ground) 10AWG in 1/2" PVC?
 
  #2  
Old 05-29-14, 06:25 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,065
Received 160 Upvotes on 146 Posts
You sure can according to the 2014 NEC.
Geo
 
  #3  
Old 05-30-14, 01:07 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
In PVC conduit, yes. Absolutely not in PVC pipe.
 
  #4  
Old 05-30-14, 04:30 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,302
Received 868 Upvotes on 731 Posts
Depending on your length of pull, I would recommend 3/4". PVC conduit can be a pain to pull in sometimes so I tend to go one size larger than normal.
 
 