NM - B outdoor


  #1  
Old 05-30-14, 09:34 AM
W
Member
Thread Starter
Join Date: Dec 2005
Location: USA
Posts: 2,931
Received 2 Upvotes on 2 Posts
NM - B outdoor

Is it OK to strip the cable jacket and paper wrap from NM - B cable and use the insulated conductors inside plastic conduit? If so, does the ground wire also need to be insulated?

I have a 2' run through conduit beneath a deck from a Jbox to a GFI.
 
  #2  
Old 05-30-14, 09:49 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
No. The wires aren't marked so they can't be used outside the sheath and they are not rated for wet use (all outside conduit is considered a wet location because it is assumed it will eventually fill with water no matter how well sealed).
 
  #3  
Old 05-30-14, 11:41 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,967
Received 192 Upvotes on 168 Posts
Move the junction box to the side of the house and bring the NM into the back of the box.
 
 