Code Question re PVC Schedule 40 capacity...

Code Question re PVC Schedule 40 capacity...
How many 20 amp circuits (12 ga THHN and grounds) can I legally install in 2" Schedule 40 PVC?
Also circuit capacity for 1 1/2" PVC?
 
Sponsored Links
  #2  
Old 05-30-14, 11:57 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,644
Why? Sounds like you need a single circuit feeding a subpanel. Tall us what your goal is and we can better help you.
 
  #3  
Old 05-30-14, 12:49 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,354
Just a note that derating will apply with multiple circuits through one conduit.
 
  #4  
Old 05-30-14, 03:34 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,981
How long is the 2" PVC pipe? If it is less than 24" it would be a nipple and derating would not apply.
 