Code Question re PVC Schedule 40 capacity...

Code Question re PVC Schedule 40 capacity...
How many 20 amp circuits (12 ga THHN and grounds) can I legally install in 2" Schedule 40 PVC?
Also circuit capacity for 1 1/2" PVC?
 
  #2  
Old 05-30-14, 12:57 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Why? Sounds like you need a single circuit feeding a subpanel. Tall us what your goal is and we can better help you.
 
  #3  
Old 05-30-14, 01:49 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,974
Received 194 Upvotes on 170 Posts
Just a note that derating will apply with multiple circuits through one conduit.
 
  #4  
Old 05-30-14, 04:34 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,301
Received 868 Upvotes on 731 Posts
How long is the 2" PVC pipe? If it is less than 24" it would be a nipple and derating would not apply.
 
 