I have a basement bathroom I am fixing up and it needs some wiring improvements. Currently two boxes, one for light switch and one for gfi outlet, plus one over head light box. Black White and ground wires running from overhead to upper outlet box and another from outlet box to switch box. Then source wires ending in outlet box.

Thr main constraint is the absurdly high placement for the upper box for the outlet because of short length of the power source wire in that box (I am okay with it though because it's a basement bathroom). I'd like to put a gfi there.

I can't figure out how to wire it all properly. Any advice would be much appreciated. Thanks
 
  #2  
Old 06-05-14, 10:38 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,824
Received 1,330 Votes on 1,229 Posts
Welcome to the forums.

Is anything already existing there ?

You have a switch box and you are installing a GFI receptacle above it.
The cable from the light should go to the switch box.
The power coming into the room should go to the GFI receptacle box.
 
  #3  
Old 06-05-14, 06:13 PM
B
Member
Thread Starter
Join Date: Jun 2014
Posts: 6
Received 0 Votes on 0 Posts
Photo

Name:  20140605_200053-1.jpg
Views: 1186
Size:  18.6 KB

Maybe this will help. This is what is currently set up. Visual helps over the explanation. All have ground by the source wire carrying the load, which just has two.
 
  #4  
Old 06-05-14, 06:51 PM
S
Member
Join Date: Apr 2014
Location: USA
Posts: 15
Received 0 Votes on 0 Posts
Keep in mind that a fluorescent light can have leakage and trip a GFCI.
 
  #5  
Old 06-05-14, 08:03 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Keep in mind that a fluorescent light can have leakage and trip a GFCI.
Moot point since best practice is to not put the lights on the GFCI.

Name:  Bg.jpg
Views: 30720
Size:  21.1 KB

Diagram based on 2011 National code. Previous code cycles would have allowed 2-conductor cable between receptacle and switch in this example with the white conductor relabeled as an ungrounded conductor.
 

Last edited by ray2047; 06-05-14 at 08:51 PM.
  #6  
Old 06-05-14, 08:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,824
Received 1,330 Votes on 1,229 Posts
Good picture.... thanks Ray.


You've got a lot of wires in the receptacle box. Makes it tough to get a GFI in.
 
  #7  
Old 06-05-14, 09:23 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,222
Received 103 Votes on 89 Posts
Go directly from the switch to the light.
 
  #8  
Old 06-05-14, 10:51 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Go directly from the switch to the light
Much cleaner but the O/P asked for:Light from receptacle box.

PCBoss' Way:

Name:  Bg 1.jpg
Views: 2812
Size:  19.2 KB
 
  #9  
Old 06-06-14, 09:44 AM
B
Member
Thread Starter
Join Date: Jun 2014
Posts: 6
Received 0 Votes on 0 Posts
Thank you all! I appreciate the advice and diagrams. Will make the job easy!
 
 