Is this sub panel wired wrong?

Reply

  #1  
Old 06-05-14, 04:50 PM
Member
Thread Starter
Join Date: Aug 2006
Location: Ambler, PA
Posts: 35
Is this sub panel wired wrong?

Hello,

Attached is a photograph of a subpanel in an outbuilding. I am told that it was wired by a professional electrician. I am confused because I thought a sub panel needed to have separate neutral and ground bus bars. Any thoughts on whether this has been wired correctly?

Thanks for the help!

Name:  panel.jpg
Views: 1132
Size:  43.6 KB
 

Last edited by PJmax; 06-05-14 at 04:59 PM. Reason: Reoriented picture
Sponsored Links
  #2  
Old 06-05-14, 04:55 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
You are right, as well as the feed must have two hots, a neutral and a grounding wire. All the neutrals to one buss, grounds to the other one. Green screw is to be removed from the buss bar and there must be a separate grounding electrode to a properly installed pair of grounding rods.

I can't make out what the red and yellow bee's nest is at the top of the box.
 
  #3  
Old 06-05-14, 05:04 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,090
That service cable coming in the top would need three insulated wires and a ground.
Those two bars currently in use should be used for neutral only and an additional bar needs to be added for the ground wires along with a ground rod.

I see SER cable coming into the top of the panel. What does that connect to outside.... a meter, a drop from the house ?

This may not be a sub panel.
 
  #4  
Old 06-05-14, 05:08 PM
Member
Thread Starter
Join Date: Aug 2006
Location: Ambler, PA
Posts: 35
Thanks for the replies. The panel in questuon is controlled by a 100 amp breaker off of the main (in a separate building).
 
  #5  
Old 06-05-14, 05:12 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,090
Ok.... then it is a sub panel and the cable connecting it is incorrect.
 
  #6  
Old 06-05-14, 07:38 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,383
I see SER cable coming into the top of the panel.
I don't see it, all I see is a SEU cable.

I am told that it was wired by a professional electrician.
I learned long ago that many electricians working for electrical contractors do not keep current with the code. A lot do, but many don't.
 
  #7  
Old 06-05-14, 08:10 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
Prior to the 08 code it was legal to feed a panel in an outbuilding with a 3 wire feeder if no metallic paths existed between the buiildings.
 
  #8  
Old 06-05-14, 08:26 PM
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 4,251
I agree with PCBoss. Depending on when it was installed and what code-cycle your locale was using at the time, the feeder could be correct.

Another issue though is that the first panel in a building needs to either 1) have a main disconnect, or 2) have fewer than 6 breakers/switches. In this case, a main-breaker panel should have been used.

Also, nowadays, a separate ground rod is required in a detached building with a panel. Though I don't know when that requirement came about.
 
  #9  
Old 06-05-14, 08:36 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,277
The panel can is not grounded as is, with the 3 wire feed. You can see the grounding strap not connected to the neutral bar.
 
  #10  
Old 06-06-14, 04:50 AM
Member
Thread Starter
Join Date: Aug 2006
Location: Ambler, PA
Posts: 35
The panel was actually installed in 2006 at which time the cable to the subpanel was run underground through plastic conduit (about 100 feet from main residence).
 
  #11  
Old 06-06-14, 09:10 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,042
The panel was actually installed in 2006
So not a code violation if no other metallic pathways. IIRC 2008 was when 4 wire required.However the six throw rule is a lot older.
cable to the subpanel was run underground through plastic conduit
Not a code compliance issue but another mark against the electrician if the conduit is continuous. Best practice is individual conductors. Makes pulling a lot easier to use individual conductors .
 

Last edited by ray2047; 06-06-14 at 09:32 AM.
  #12  
Old 06-06-14, 02:25 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
SE-U cable cannot be used underground.
 