Ground fault?


  #1  
Old 06-10-14, 02:47 PM
C
Member
Thread Starter
Join Date: Nov 2013
Posts: 213
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ground fault?

Circuit that contains a couple of can lights and two outlets.

I can test continuity (audible alarm) while power is on with my multimeter. I have continuity at the outlets between ground and neutral with the power on but the lights off. When you switch the lights on, there is no audible alarm (ie no continuity.

With the breaker off, there is constant continuity between neutral and ground at the outlets.

Do I have a ground fault on this circuit?
 
  #2  
Old 06-10-14, 04:22 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,608
Upvotes: 0
Received 9 Upvotes on 8 Posts
You can't test continuity with power applied. The breaker being on or off will not have anything to do with continuity to the neutral/ground bus in the panel. What prompted you to do this check? Are you having problems? If so, describe them.
 
  #3  
Old 06-10-14, 04:42 PM
C
Member
Thread Starter
Join Date: Nov 2013
Posts: 213
Upvotes: 0
Received 0 Upvotes on 0 Posts
You can't test continuity with power applied.
Yes, certain meters have this function. The low impendence meters can do this.

With that said... there should always be continuity between ground and neutral at an outlet (whether you check with power on or off) since they are bonded in the panel... is that a fair assessment?

Or would you not be able to detect the bond upstream of the panel?
 
  #4  
Old 06-10-14, 04:48 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Please tell us your problem. So far we have some questionable testing but nothing to tell us the problem is.
 
  #5  
Old 06-10-14, 04:50 PM
C
Member
Thread Starter
Join Date: Nov 2013
Posts: 213
Upvotes: 0
Received 0 Upvotes on 0 Posts
Not sure if I have a problem to report Ray... hence the question.
 
  #6  
Old 06-10-14, 04:58 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Since ground and neutral at the first OCPD are connected together you should see continuity. If connected to a service panel other than the first OCPD and wired according to NEC 2008 or later you may see a slight resistance depending on soil conductivity and other unknowns.
 
  #7  
Old 06-10-14, 05:03 PM
C
Member
Thread Starter
Join Date: Nov 2013
Posts: 213
Upvotes: 0
Received 0 Upvotes on 0 Posts
So the neutral/ground bond I am seeing at the outlet on a branch circuit is normal since they are bonded together at the panel?
 
  #8  
Old 06-10-14, 05:09 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Yes.

.
 
  #9  
Old 06-10-14, 05:31 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
You can also see continuity from hot to neutral through an incandescent light bulb.
 
  #10  
Old 06-10-14, 07:18 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,753
Received 672 Upvotes on 570 Posts
A ground fault is when current bypasses the neutral wire and leaks to ground. You are only measuring continuity, not current.
 
 