Tripping circuit breaker


  #1  
Old 06-10-14, 03:30 PM
L
Member
Thread Starter
Join Date: Jun 2014
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Tripping circuit breaker

I'm am at my wits end. I purchased a newly constructed 3BR/2.5BA home in 2011. One of the bedroom we use as an office. The breaker in this room will trip/blow at least 3-5 times a week. I can never reproduce what makes it trip and it's completely random. I've had an electrician replace the breaker twice because he said that sometimes they come faulty from the manufacturer.

In our office we have our computer (monitor, modem, printer), phone, 42" flat panel TV, PS3, and an audio receiver with a powered subwoofer. There are times when I can be on the computer surfing the web, playing PS3, with the audio equipment on and have the ceiling fan and lights on and nothing happens. Other times I can have the TV off, audio equipment off, PS3 off, lights and fan off, and just be working on the PC and the breaker will blow. Vice versa, I can have the PC shutdown, monitor off, printer off, and just watching TV or playing PS3 and it trips.

I'm completely puzzled Any help or suggestions at this point would be more than welcome.
 
  #2  
Old 06-10-14, 04:17 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,608
Upvotes: 0
Received 9 Upvotes on 8 Posts
Welcome to the forums. When it happens again, check the rest of the house, garage, basement, etc to see if anything else loses power. You may have something, like a small refrigerator that powers on intermittently that will cause an overload.
 
  #3  
Old 06-10-14, 05:28 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
A house that new should have AFCI protection.
 
  #4  
Old 06-10-14, 05:32 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,608
Upvotes: 0
Received 9 Upvotes on 8 Posts
Good catch, Jim. It doesn't take much to trip one. I would eliminate one piece of electronics at a time to see if it continues.
 
  #5  
Old 06-10-14, 06:21 PM
L
Member
Thread Starter
Join Date: Jun 2014
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the replies. I spoke to an electrician earlier today and he is coming to check out the problem. He mentioned arc-fault but I'm not sure if those are installed or not, but hopefully he will solve the problem.

I'll be sure to check the rest of the house if it trips between now and the time he comes, to see if any power hungry electronics or appliances kick on or off.
 
  #6  
Old 06-10-14, 06:25 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
AFCIs look for arcs from loose connections.
 
  #7  
Old 06-10-14, 07:21 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,752
Received 673 Upvotes on 571 Posts
I did a service call once and found a surge protector that was causing an AFCI to trip. Looking on the web confirmed that some older surge protectors can cause issues. If you have one (or more) try bypassing it.
 
  #8  
Old 06-11-14, 05:09 AM
R
Member
Join Date: May 2013
Location: USA
Posts: 138
Upvotes: 0
Received 0 Upvotes on 0 Posts
Tolyn Ironhand - The reason I love sites like this one; I did not know about that surge protectors. Thank you for sharing. Roger
 
  #9  
Old 06-11-14, 05:31 AM
D
Member
Join Date: Sep 2013
Posts: 46
Upvotes: 0
Received 0 Upvotes on 0 Posts
Depending on the OP's location...a house built in 2011 could have been inspected under the 2005 code cycle or possibly even the 2002 as some states do not adopt the more current ones. In NY where I am we just recently came off of the 2005 and are currently on the 2008. Depending on the code cycle it was inspected under, Arc faults may not have been required unless local amendments required them.
 
  #10  
Old 06-11-14, 08:53 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
Depending on the OP's location...a house built in 2011 could have been inspected under the 2005 code cycle or possibly even the 2002 as some states do not adopt the more current ones.
The 2002 NEC required AFCI protection of all 120 volt bedroom circuits of 15 or 20 amps.
 
 