Need help with GFI receptacle that won't work

Can't get GFI receptacle to work. Black to gnd = 120v. Black to white = 120v. White to gnd = 0.2v. Hooking black to brass "line" screw, and white to silver "line" screw. Receptacle is dead. Test / reset does nothing. What is problem?
 
  #2  
Old 06-14-14, 06:22 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Try a different GFCI.

.
 
  #3  
Old 06-15-14, 04:24 AM
J
Member
Thread Starter
Join Date: Jun 2014
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Still have GFI problem

I have tried a brand new GFI receptacle. Still doesn't work.
Could I have neutral wire "partially shorted to ground somewhere? What to measure. Continuity and/or resistance (ohms) between white and ground with power off?
 
  #4  
Old 06-15-14, 04:47 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Your voltage reading are correct. Are you using the line terminals?
 
  #5  
Old 06-15-14, 05:27 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 6,095
Received 422 Upvotes on 375 Posts
Hooking black to brass "line" screw, and white to silver "line" screw
Assuming your ground/bare wire is connected to the green screw as well?

It's normal and expected for white/neutral to ground voltage readings to be 0v (or really close). So you're good there.

Are you sure you're pressing the reset button in far enough? I've found newer models have to be pressed in further to actually reset.
 
  #6  
Old 06-15-14, 01:52 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 9 Upvotes on 8 Posts
A GFCI doesn't need a ground to work properly. I measures the differential between the hot and neutral in milliamps. When that differential exceeds a threshold, it trips out. Check to make sure you have continuity from your neutral to the ground.
 
 