100A meter panel w/ disconnect 320 feet to mobile home 100A panel w/disconnect

I am in a very unpopulated rural area and am installing a feed from a pole with a meter and panel with a 100A service disconnect breaker to run about 320' to a newly placed mobile home with a panel that has a 100A main disconnect.

Both disconnect breakers are rated for CU/AL.

I believe I should run four conductors, probably using aluminum mobile home feeder cable such as supplied by Southwire.

I would use NOALOX or equivalent anti-oxidation grease at the termination points.

I plan to run the cable buried 20 inches underground in schedule 40 PVC electrical grade conduit to provide extra physical protection. I would use factory bent PVC risers at either end.

The neutral is bonded to ground at the meter panel. I would keep them separate at the mobile home (as they were previously wired) but would add one properly installed ground rod.

Southwire specifies their 2-2-4-6 AL-Mobile Home Feeder cable for 100A but I am quite certain I should use heavier wire for such a long run.

Could you advise me regarding the properly sized cable for this project, the proper size conduit for it, and anything else I should watch out for?

Finally - Home Depot may carry the cable in 500' rolls but it is pricey. Any tips on the least expensive way or place to purchase such a length?

Many thanks in advance. I have read through quite a number of related threads and appreciate all the help you all have been providing folks!
 
Sponsored Links
  #2  
Old 06-11-14, 03:52 PM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,755
Received 42 Votes on 40 Posts
Use 3/O aluminum conductors for this distance (700' round trip) to lose no more than 3% or 7.2 volts along the way.

Install two 8' ground rods at least 6' apart at the mobile home panel.

In a conduit you can run single conductors as opposed to multi-conductor cable which may make it easier to buy just how much you need. The wire must be wet environment rated such as THWN.
 
  #3  
Old 06-11-14, 06:09 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,057
Received 73 Votes on 65 Posts
Remember that voltage drop is dictated by load. If there is no load, there is no voltage drop.

Since we don't know what the expected load will be, I would assume somewhere around 60 amp load. (I base this on experience, nothing more). If you were to use this cable: Southwire 2-2-4-6 Aluminum MHF Wire (By-the-Foot)-30163099 at The Home Depot which HD sells by the foot, here are the results:

Voltage drop: 9.46
Voltage drop percentage: 3.94%
Voltage at the end: 230.54
 
  #4  
Old 06-11-14, 07:28 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,280
Received 43 Votes on 35 Posts
I plan to run the cable buried 20 inches underground in schedule 40 PVC electrical grade conduit to provide extra physical protection. I would use factory bent PVC risers at either end.
I see no good reason at all to run the feeder in conduit other than a conduit riser at the service pole and at the mobile home. If you aren't going to direct bury it, why spend the extra dollars on direct burial wire? If you just want to use a complete run of conduit, don't buy the mobile home feeder, but go to a supply house and buy what you need in aluminum Type XHHW.
 
  #5  
Old 06-11-14, 08:02 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,057
Received 73 Votes on 65 Posts
I missed the part where the OP wants to use conduit. 320' pull in PVC? that is going to be one heck of a pull! I suggest upping your conduit size by one and use steel 90's.

I would also just use direct burial MH feeder.
 
  #6  
Old 06-12-14, 07:47 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,280
Received 43 Votes on 35 Posts
320' pull in PVC? that is going to be one heck of a pull!
Yep, that's a difficult pull for a pro. The mobile home feeder also has a slight twist from the factory to keep the conductors together for direct burial installations which adds resistance and makes pulling in conduit twice as hard. I believe if I were going to try it I'd use conduit at least 2 sizes bigger than normal.
 
  #7  
Old 06-12-14, 12:41 PM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
Received 1 Vote on 1 Post
You'll also need to add a disconnect, adjacent to and not attached to, the mobile home. It needs to be within sight and can't be more than 30' away.
 
  #8  
Old 07-14-14, 12:58 PM
Member
Thread Starter
Join Date: Jun 2014
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
The feed installation is complete. The mobile home is being converted to a permanent home on a foundation thus the 4-wire feed was run from the 100 A 240 V breaker on the pole 310 feet to the 100 A breaker on the panel inside the home. It was buried 30" over most of the route.

I found a source of new twisted cable short ends on Amazon and bought a 350' roll of 2/0 2/0 2/0 1 twisted direct burial aluminum cable. However I wanted it to have further protection and put it in 2" PVC conduit with sweeps at each end. The #1 cable is used for ground. I am installing two 8' ground rods with proper clamps adjacent to the mobile home panel tied to the grounding strip. Neutral and ground are bonded only at the meter panel.

The 2/0 would not fit in the breakers at either end so I used CU-AL approved split bolts and #1 copper pigtails to tie into the breakers. Antioxidant on all aluminum connections. The split bolts are wrapped with multiple layers of 3M rubber electrical tape.

Thank you to all who submitted comments on this installation.
 
  #9  
Old 07-14-14, 02:36 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Sounds good. Thanks for letting us know how it was finished.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: