Installed RV outlet - Neutral lash up questionable-- Need expert advice
#1
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Installed RV outlet - Neutral lash up questionable-- Need expert advice
RV outlet is 70 feet from 60 Amp duplex breaker in sub-panel. Ran 4 ea #6 single strand copper thru 1" electrical PVC. Plan was to install a 50 amp RV outlet. After running the wire, I decided to install 2 ea 30 amp RV outlets instead of one 50 Amp. So, I used the #6 (white neutral wire) as "common" for both circuits! It works fine but I'm having 2nd thoughts about using the same neutral wire for both circuits.
With different phases of 115 vac on the same return line I wonder if both RV outlets are in use, will it will develop voltage on the neutral at the RV end? Will this cause a problem?
What does the NEC code say about this? :NO NO NO:
And last, why do I need a duplex breaker? (obviously, I don't!)
Thanks in advance for any help!
With different phases of 115 vac on the same return line I wonder if both RV outlets are in use, will it will develop voltage on the neutral at the RV end? Will this cause a problem?

What does the NEC code say about this? :NO NO NO:
And last, why do I need a duplex breaker? (obviously, I don't!)

Thanks in advance for any help!
#2
The breaker size needs to be 30 amps.
You have a multiwire circuit. No problem as long as the hots or on opposite legs. NEC requires either a two pole breaker or two handle tied single pole breakers.
I wonder if both RV outlets are in use, will it will develop voltage on the neutral at the RV end?
#4
The multiwire branch circuit with two 30 amp RV receptacles, one on each leg, behaves the same way as a 120/240 volt circuit serving a single 50 amp receptacle (except for the rating of the breaker serving the circuit which may not exceed the receptacle rating). In both cases the neutral current will be the difference of the current draws on the two hot legs so it will never exceed either of the hot conductor currents.
By installing a sub-subpanel* at the RV location you could have both a 120/240 volt receptacle and one or two 120 volt 30 amp receptacles using the existing feed conductors.
* Subpanel is not an officially recognized term in the National Electric Code.
By installing a sub-subpanel* at the RV location you could have both a 120/240 volt receptacle and one or two 120 volt 30 amp receptacles using the existing feed conductors.
* Subpanel is not an officially recognized term in the National Electric Code.
#6
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Okay, actually my breaker is 2-pole 30A for a total of 60A. Does it have to be 2-pole or could I replace it with 2 singlle pole 30A breakers and still meet NEC requirements? (My background is electronics and I don't have a good grasp of the electrician lingo and jargon.) Thanks for your help!
#7
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the reply. I used #6 because my brother gave me a 500' roll. The price was right! I also added several 20A outlets in my garage using #12 conductors a #14 ground. Is #14 adequate for those?
#8
Okay, actually my breaker is 2-pole 30A for a total of 60A.
Does it have to be 2-pole or could I replace it with 2 singlle pole 30A breakers
#9
Does it have to be 2-pole or could I replace it with 2 singlle pole 30A breakers and still meet NEC requirements?
I also added several 20A outlets in my garage using #12 conductors a #14 ground. Is #14 adequate for those?
#10
Your egc for the 20 amp circuit should be green or bare #12. The egc does not drop in size until larger circuits.
#15
I used 20 Amp duplex receptacles on two single pole 20 Amp breakers (2 circuits). There is an existing GFCI 20 circuit in the garage that is separate.