I know I have been down this road before on this forum, but I have finally built my AG pool and have a 1.5hp filter pump running. However, it's running temporarily via an extension cord (that I disconnect when not in use) and I would like to install a subpanel ASAP. Can anyone suggest a good outdoor panel that has single phase 120V and possibly room for a standard 15-amp outlet? Of course it will have to be able to support GFCI breakers as well.
#4
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Possibly this one:
Intermatic Controls & Timers - Swimming Pool Supplies, Parts, and more - Backyard Pool Superstore
T21001R model
Thoughts?
Intermatic Controls & Timers - Swimming Pool Supplies, Parts, and more - Backyard Pool Superstore
T21001R model
Thoughts?
Last edited by StoningtonQB; 07-10-14 at 10:39 AM.
#8
It isn't U.L. Listed, I wouldn't use it
I've never used one of the Intermatic panels you posted, but I've seen them installed and they're pretty nice.
#9
Member
Thread Starter
Join Date: Sep 2013
Location: USA
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It says right on the spec sheet it's CSA (C-US) listed. It may not be UL, but it's still a NRTL.
I've never used one of the Intermatic panels you posted, but I've seen them installed and they're pretty nice.
I've never used one of the Intermatic panels you posted, but I've seen them installed and they're pretty nice.
One more question for all the experts, not pertaining to this particular panel but a wiring question in general:
As I pull my THHN / THWN through conduit, should I pull a ground wire as well? I ask this because 1) I'm not certain if my neutrals in the main breaker panel are isolated from the grounds (I will check). 2) If the worst happens, and disaster strikes, will it affect the main breaker negatively if the two panels are grounded together?
This panel will have its own grounding rods. Would it make sense to join grounds? I could use a little direction on this part!
#10
Pull an insulated ground. The neutrals and grounds MUST be separate in a sub panel. Also if this is for a pool or feeding receptacles, everything must be GFCI protected.