Baseboard heater installation in the bathroom

I think I have this correct but I'd like to verify.

I'm going to install a 30 inch, 120v, 500 watt baseboard heater in my 36 square foot bathroom.

The amps (per my calculation) is 4.16 amps and 5.2 amps continuous. If this is the only thing on this circuit (and it will be) it seems that I could put this on a 15 amp circuit, with 14/2 wire. Is that correct?

And I presume that even with a heater this small, and the apparent excess in amps available, that I can't put anything else on this circuit such as an outlet, right?

Am I missing anything?

Thanks in advance for any assistance!
 
Sponsored Links
  #2  
Old 07-10-14, 09:31 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,277
Welcome to the forums.

A receptacle and that heater can be on the same 15A circuit. However, that doesn't include a receptacle in the bathroom, which should be on its own separate 20A circuit.
 
  #3  
Old 07-10-14, 09:34 AM
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 18,172
The killer is "bathroom". I do not think electric baseboard heaters are permitted in a bathroom.
 
  #4  
Old 07-10-14, 09:35 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,405
The amps (per my calculation) is 4.16 amps and 5.2 amps continuous. If this is the only thing on this circuit (and it will be) it seems that I could put this on a 15 amp circuit, with 14/2 wire. Is that correct?
The amps would be 4.1666666. Where did you get 5.2 amps? 14-2 NM-B cable on a 15 amp breaker would work. I wouldn't put anything else on this circuit. Considering the small size of the room, I'd probably go with a radiant wall heater.
 
  #5  
Old 07-10-14, 09:53 AM
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 13
I got to 5.2 amps because I thought that a heater had to have a "continuous" rating of 125% for the base calculation. I could have that wrong.

PJMax, thanks for the welcome and info.
 
  #6  
Old 07-10-14, 10:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,277
When you pick out the unit you are going to use..... make sure it states ok for bathrooms or conversely.... not ok for bathrooms. I would also install it connected to a GFCI breaker.
 