Baseboard heater installation in the bathroom


  #1  
Old 07-10-14, 09:16 AM
S
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Baseboard heater installation in the bathroom

I think I have this correct but I'd like to verify.

I'm going to install a 30 inch, 120v, 500 watt baseboard heater in my 36 square foot bathroom.

The amps (per my calculation) is 4.16 amps and 5.2 amps continuous. If this is the only thing on this circuit (and it will be) it seems that I could put this on a 15 amp circuit, with 14/2 wire. Is that correct?

And I presume that even with a heater this small, and the apparent excess in amps available, that I can't put anything else on this circuit such as an outlet, right?

Am I missing anything?

Thanks in advance for any assistance!
 
  #2  
Old 07-10-14, 09:31 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,663
Received 3,899 Upvotes on 3,495 Posts
Welcome to the forums.

A receptacle and that heater can be on the same 15A circuit. However, that doesn't include a receptacle in the bathroom, which should be on its own separate 20A circuit.
 
  #3  
Old 07-10-14, 09:34 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 27,533
Received 2,122 Upvotes on 1,899 Posts
The killer is "bathroom". I do not think electric baseboard heaters are permitted in a bathroom.
 
  #4  
Old 07-10-14, 09:35 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,870
Received 185 Upvotes on 166 Posts
The amps (per my calculation) is 4.16 amps and 5.2 amps continuous. If this is the only thing on this circuit (and it will be) it seems that I could put this on a 15 amp circuit, with 14/2 wire. Is that correct?
The amps would be 4.1666666. Where did you get 5.2 amps? 14-2 NM-B cable on a 15 amp breaker would work. I wouldn't put anything else on this circuit. Considering the small size of the room, I'd probably go with a radiant wall heater.
 
  #5  
Old 07-10-14, 09:53 AM
S
Member
Thread Starter
Join Date: Jul 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
I got to 5.2 amps because I thought that a heater had to have a "continuous" rating of 125% for the base calculation. I could have that wrong.

PJMax, thanks for the welcome and info.
 
  #6  
Old 07-10-14, 10:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,663
Received 3,899 Upvotes on 3,495 Posts
When you pick out the unit you are going to use..... make sure it states ok for bathrooms or conversely.... not ok for bathrooms. I would also install it connected to a GFCI breaker.
 
 