Welder wiring

Sorry for another welder wiring question but want to make sure I have correct wire. Welder says 240v 60hz 20amp with 110a at 20% cycle rate. I have a 50 amp breaker (welder plug is 6-50P) and have some awg 8/2 (with ground). Can I use this 8/2 for welder only outlet safely. From panel to outlet is less than 10 feet. Going to replace wire on welder with same plug but add a 15' cord. So will this be safe and correct? Does wire from panel (in wall) have to be ran in anything like plastic tube? Thanks for help.
 
  #2  
Old 07-13-14, 11:48 AM
S
Member
Join Date: Jul 2014
Posts: 36
Upvotes: 0
Received 0 Upvotes on 0 Posts
I am no electrician but i do weld. Appears you have a small mig machine similar to my 175 miller. Those are 20amp 220 machines, not like the old 50amp service for the buzz boxes of years ago. As recommended, suitable receptacle and sub panel will get you going.
 
  #3  
Old 07-13-14, 02:53 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
Welcome to the forums!

Your welder is a 20 amp 240 volt unit. 8/s is overkill for that welder but will work if that is all you have. Max breaker size for 8/2 is 40 amps.
 
  #4  
Old 07-13-14, 06:31 PM
H
Member
Thread Starter
Join Date: Jul 2014
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for all the info. Not sure why they put the 50 amp plug on all the welders. I figure it will be overkill but because manual called for using 50 amp breaker I will run the 50amp with 6/2 from breaker to outlet. If you mind just one more question can I use 6/3 and leave neutral capped at box and outlet. This would give me option later to run anything I may need that I don't know about now. Thanks again for everyone's help.
 
  #5  
Old 07-13-14, 06:51 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
If you mind just one more question can I use 6/3 and leave neutral capped at box and outlet. This would give me option later to run anything I may need that I don't know about now.
Yes. That would be a very good option. I have never seen a welder that requires a neutral, but 6/3 would cover all the bases.
 
 