installing a 100 amp sub panel, distance requires 4/0 conductors, the 100 amp breakers will not accept the 4/0, are there adapter lugs available to resolve this issue?
#2
installing a 100 amp sub panel, distance requires 4/0 conductors, the 100 amp breakers will not accept the 4/0, are there adapter lugs available to resolve this issue?
#5
Member
Join Date: Oct 2013
Location: United States
Posts: 189
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Feeder
310.15B(7)(2) cannot be used for a dwelling feeder where the feeder does not carry the entire dwelling load. That being said, unless your feeder will be operating at a very high demand I don't see a requirement for #4/0 AL.
#1/0 AL with an 80 amp load would be a 2.94% Volt Drop. #1/0 will probably fit into your breaker.
If you have the #4/0 already installed then as suggested, install a junction box and reduce the conductor at each end for a short distance into the panels for termination.
#1/0 AL with an 80 amp load would be a 2.94% Volt Drop. #1/0 will probably fit into your breaker.
If you have the #4/0 already installed then as suggested, install a junction box and reduce the conductor at each end for a short distance into the panels for termination.