No breaker flipped but power out in master bedroom and bathroom.
HELP!
My daughter was playing with the switch in the bathroom and the power went out in the bathroom and bedroom. I went out to the circuit box, and nothing was flipped. I switched the master bedroom switch off and back on and still no power. Am I missing something? This happened before in the other bathroom, but my husband can't remember what he did to fix it and I can't find any answers online.
My daughter was playing with the switch in the bathroom and the power went out in the bathroom and bedroom. I went out to the circuit box, and nothing was flipped. I switched the master bedroom switch off and back on and still no power. Am I missing something? This happened before in the other bathroom, but my husband can't remember what he did to fix it and I can't find any answers online.
#2
How old is the house? Bath and bedroom should not be on the same breaker. Have you checked all GFCIs inside and outside the house? You will need check connections in all boxes. Move any back stabs to the screws and redo all wire nut connections starting with the switch. Have you read: http://www.doityourself.com/forum/el...ther-info.html
#3
Welcome to the forums! It is possible one GFCI is working both bathrooms. Check all the GFCIs. Make sure you turn the breaker to the bathroom/bedroom completely off, then back on. Sometimes they won't appear to be tripped, but actually are.
#4
Member
Thread Starter
Join Date: Jul 2014
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
New House
Ray, the house is only a little over 2 years old. I'm assuming it's the bedroom and the master bathroom together. The box doesn't have the master bathroom labeled separately.
None of the outlets in our bathroom or bedroom are GFCI's. Now what???
None of the outlets in our bathroom or bedroom are GFCI's. Now what???
#5
You may not have found the correct breaker. A 2 year old house should have a dedicated 20 amp breaker for the bathroom. It is required by national code recommendations usually adopted locally. Turn every 20 amp breaker fully off then back on regardless of the labeling (often wrong) and if that doesn't fix it try all the 15 amp single pole breakers.
#6
New House
Ray, the house is only a little over 2 years old. I'm assuming it's the bedroom and the master bathroom together. The box doesn't have the master bathroom labeled separately.
None of the outlets in our bathroom or bedroom are GFCI's. Now what???
Ray, the house is only a little over 2 years old. I'm assuming it's the bedroom and the master bathroom together. The box doesn't have the master bathroom labeled separately.
None of the outlets in our bathroom or bedroom are GFCI's. Now what???
#7
With a house that new, I say definitely a violation. Stacked bathrooms can have one GFCI operating all the receptacles, but you can't add bathroom lights. Definitely not bedroom lights on same circuit. Good point CJ. Do need profile completed, please.